    Daisy Chain Ubiquiti AC Pros?

    IT Discussion
    ubnt wifi access point ubiquiti wireless ap networking
    8
    75
    7.4k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • DustinB3403D
      DustinB3403 @dafyre
      last edited by

      @dafyre I think the goal is to not have to house equipment in otherwise rentable space.

      If that cabin is occupied and there is an issue, you're invading a clients rented space.

      1 Reply Last reply Reply Quote 0
      • Mike DavisM
        Mike Davis
        last edited by

        @dafyre said in daisy chain Ubiquiti AC Pros?:

        Edit: I don't see any practical way to do this without having to run some cable.

        yes, I plan on running cable.

        Sorry, the reason I picked the AC Pro is it has the second ethernet port that I understood was for Ethernet pass through in applications like this. It's not PoE pass though, just ethernet.

        DustinB3403D 1 Reply Last reply Reply Quote 0
        • DustinB3403D
          DustinB3403
          last edited by

          I would honestly just run conduit to each location and have everything connect back at the main house.

          It's not that much effort, and PVC is stupidly cheap.

          Mike DavisM 1 Reply Last reply Reply Quote 0
          • DustinB3403D
            DustinB3403 @Mike Davis
            last edited by

            @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

            @dafyre said in daisy chain Ubiquiti AC Pros?:

            Edit: I don't see any practical way to do this without having to run some cable.

            yes, I plan on running cable.

            Sorry, the reason I picked the AC Pro is it has the second ethernet port that I understood was for Ethernet pass through in applications like this. It's not PoE pass though, just ethernet.

            It is, but this isn't as if you're setting up your home and can deal with the side effects of chained APs.

            For the APs 10 and 11 I could see making this usable, but I wouldn't do it for the rest of the space.

            Mike DavisM 1 Reply Last reply Reply Quote 0
            • Mike DavisM
              Mike Davis @DustinB3403
              last edited by

              @DustinB3403 said in daisy chain Ubiquiti AC Pros?:

              I would honestly just run conduit to each location and have everything connect back at the main house.

              It's not that much effort, and PVC is stupidly cheap.

              The more I think about it, I don't need 1" the entire run, only to the first cottage and then I can leave that cottage with 3/4" to the next one and so on. The only concern then is the distance. The labor to trench is the same no matter the size of the conduit. (at these sizes)

              DashrenderD 1 Reply Last reply Reply Quote 1
              • DashrenderD
                Dashrender @Mike Davis
                last edited by

                @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

                @DustinB3403 said in daisy chain Ubiquiti AC Pros?:

                I would honestly just run conduit to each location and have everything connect back at the main house.

                It's not that much effort, and PVC is stupidly cheap.

                The more I think about it, I don't need 1" the entire run, only to the first cottage and then I can leave that cottage with 3/4" to the next one and so on. The only concern then is the distance. The labor to trench is the same no matter the size of the conduit. (at these sizes)

                Is the price difference here really that bad from 1" to 3/4"?

                coliverC 1 Reply Last reply Reply Quote 0
                • Mike DavisM
                  Mike Davis @DustinB3403
                  last edited by

                  @DustinB3403 said in daisy chain Ubiquiti AC Pros?:

                  For the APs 10 and 11 I could see making this usable, but I wouldn't do it for the rest of the space.

                  haha, 10 will actually have a switch because I need the SFP to convert from fiber to copper.

                  1 Reply Last reply Reply Quote 0
                  • coliverC
                    coliver @Dashrender
                    last edited by

                    @Dashrender said in daisy chain Ubiquiti AC Pros?:

                    @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

                    @DustinB3403 said in daisy chain Ubiquiti AC Pros?:

                    I would honestly just run conduit to each location and have everything connect back at the main house.

                    It's not that much effort, and PVC is stupidly cheap.

                    The more I think about it, I don't need 1" the entire run, only to the first cottage and then I can leave that cottage with 3/4" to the next one and so on. The only concern then is the distance. The labor to trench is the same no matter the size of the conduit. (at these sizes)

                    Is the price difference here really that bad from 1" to 3/4"?

                    Not a significant amount. Just run 1" the entire way. You'll have room for expansion in the future if need be.

                    Mike DavisM 1 Reply Last reply Reply Quote 0
                    • DustinB3403D
                      DustinB3403
                      last edited by

                      How deep does this conduit need to be buried?

                      1 Reply Last reply Reply Quote 0
                      • Mike DavisM
                        Mike Davis @coliver
                        last edited by

                        @coliver said in daisy chain Ubiquiti AC Pros?:

                        @Dashrender said in daisy chain Ubiquiti AC Pros?:

                        @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

                        @DustinB3403 said in daisy chain Ubiquiti AC Pros?:

                        I would honestly just run conduit to each location and have everything connect back at the main house.

                        It's not that much effort, and PVC is stupidly cheap.

                        The more I think about it, I don't need 1" the entire run, only to the first cottage and then I can leave that cottage with 3/4" to the next one and so on. The only concern then is the distance. The labor to trench is the same no matter the size of the conduit. (at these sizes)

                        Is the price difference here really that bad from 1" to 3/4"?

                        Not a significant amount. Just run 1" the entire way. You'll have room for expansion in the future if need be.

                        $4.21 vs $2.71. You guys are right. On a project this size the difference would be under $100. It would cost way more to have to go back and dig for another run.

                        coliverC 1 Reply Last reply Reply Quote 0
                        • coliverC
                          coliver @Mike Davis
                          last edited by

                          @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

                          @coliver said in daisy chain Ubiquiti AC Pros?:

                          @Dashrender said in daisy chain Ubiquiti AC Pros?:

                          @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

                          @DustinB3403 said in daisy chain Ubiquiti AC Pros?:

                          I would honestly just run conduit to each location and have everything connect back at the main house.

                          It's not that much effort, and PVC is stupidly cheap.

                          The more I think about it, I don't need 1" the entire run, only to the first cottage and then I can leave that cottage with 3/4" to the next one and so on. The only concern then is the distance. The labor to trench is the same no matter the size of the conduit. (at these sizes)

                          Is the price difference here really that bad from 1" to 3/4"?

                          Not a significant amount. Just run 1" the entire way. You'll have room for expansion in the future if need be.

                          $4.21 vs $2.71. You guys are right. On a project this size the difference would be under $100. It would cost way more to have to go back and dig for another run.

                          That's actually more then it used to be. When I worked in a hardware store it was pennies a linear foot difference... and we weren't getting the bulk rate. But either way for under 100$ trench the 1" pipe and not worry about it.

                          1 Reply Last reply Reply Quote 1
                          • DustinB3403D
                            DustinB3403
                            last edited by

                            @Mike-Davis how deep are you burying this conduit? Why not just rent the trencher yourself and get this done in a day?

                            Mike DavisM 1 Reply Last reply Reply Quote 0
                            • JaredBuschJ
                              JaredBusch
                              last edited by

                              Mike,
                              I think this whole this is super confused right now.

                              Why is there copper involved? All of this should be fiber.

                              Are these copper and fiber runs listed already in place ? Or are they being planned?

                              Start this whole thing over...

                              Mike DavisM 1 Reply Last reply Reply Quote 0
                              • Mike DavisM
                                Mike Davis @DustinB3403
                                last edited by

                                @DustinB3403 The guy that owns the place will run all the conduit. I vacation there. I'd rather be on vacation than digging a ditch. They will probably only need me to terminate everything and configure it.

                                DustinB3403D 1 Reply Last reply Reply Quote 1
                                • DustinB3403D
                                  DustinB3403 @Mike Davis
                                  last edited by

                                  @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

                                  @DustinB3403 The guy that owns the place will run all the conduit. I vacation there. I'd rather be on vacation than digging a ditch. They will probably only need me to terminate everything and configure it.

                                  So why the F does the price of burying conduit matter? Who brought up this point?

                                  Just run 1" throughout, since it's not costing your bottem line.

                                  JaredBuschJ 1 Reply Last reply Reply Quote 0
                                  • JaredBuschJ
                                    JaredBusch @DustinB3403
                                    last edited by

                                    @DustinB3403 said in daisy chain Ubiquiti AC Pros?:

                                    @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

                                    @DustinB3403 The guy that owns the place will run all the conduit. I vacation there. I'd rather be on vacation than digging a ditch. They will probably only need me to terminate everything and configure it.

                                    So why the F does the price of burying conduit matter? Who brought up this point?

                                    Just run 1" throughout, since it's not costing your bottem line.

                                    It has a cost. because it is not his costs does not matter.

                                    Mike DavisM 1 Reply Last reply Reply Quote 0
                                    • Mike DavisM
                                      Mike Davis @JaredBusch
                                      last edited by

                                      @JaredBusch said in daisy chain Ubiquiti AC Pros?:

                                      Mike,
                                      I think this whole this is super confused right now.

                                      Why is there copper involved? All of this should be fiber.

                                      Are these copper and fiber runs listed already in place ? Or are they being planned?

                                      Start this whole thing over...

                                      The only thing they have now is internet to the Main House (1). I thought copper would be less expensive than fiber since I would only need a $20 circuit protector on it, vs a switch with a SFP if fiber is run. Also with fiber, can't terminate it myself, so that would mean hiring that out, or ordering premade cables at the right lengths.

                                      DustinB3403D JaredBuschJ 2 Replies Last reply Reply Quote 0
                                      • Mike DavisM
                                        Mike Davis @JaredBusch
                                        last edited by

                                        @JaredBusch said in daisy chain Ubiquiti AC Pros?:

                                        It has a cost. because it is not his costs does not matter.

                                        Right, since I vacation there, the cost goes in to rental fees going up, or the project just not getting started because they can't absorb the cost.

                                        1 Reply Last reply Reply Quote 0
                                        • DustinB3403D
                                          DustinB3403 @Mike Davis
                                          last edited by

                                          @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

                                          @JaredBusch said in daisy chain Ubiquiti AC Pros?:

                                          Mike,
                                          I think this whole this is super confused right now.

                                          Why is there copper involved? All of this should be fiber.

                                          Are these copper and fiber runs listed already in place ? Or are they being planned?

                                          Start this whole thing over...

                                          The only thing they have now is internet to the Main House (1). I thought copper would be less expensive than fiber since I would only need a $20 circuit protector on it, vs a switch with a SFP if fiber is run. Also with fiber, can't terminate it myself, so that would mean hiring that out, or ordering premade cables at the right lengths.

                                          But you already are going to have to hire someone to terminate the 1 fiber cable for APs 10 and 11. Might as well just keep the tech around and have them terminate it all.

                                          Mike DavisM 1 Reply Last reply Reply Quote 0
                                          • JaredBuschJ
                                            JaredBusch @Mike Davis
                                            last edited by

                                            @Mike-Davis said in daisy chain Ubiquiti AC Pros?:

                                            @JaredBusch said in daisy chain Ubiquiti AC Pros?:

                                            Mike,
                                            I think this whole this is super confused right now.

                                            Why is there copper involved? All of this should be fiber.

                                            Are these copper and fiber runs listed already in place ? Or are they being planned?

                                            Start this whole thing over...

                                            The only thing they have now is internet to the Main House (1). I thought copper would be less expensive than fiber since I would only need a $20 circuit protector on it, vs a switch with a SFP if fiber is run. Also with fiber, can't terminate it myself, so that would mean hiring that out, or ordering premade cables at the right lengths.

                                            But copper is also going to be prone to more issues like interference.

                                            But that is a cost versus cost versus risk that has to be assessed.

                                            This entire thing needs stopped and taken back to basics.

                                            1. What is the goal
                                            DustinB3403D 1 Reply Last reply Reply Quote 1
                                            • 1
                                            • 2
                                            • 3
                                            • 4
                                            • 2 / 4
                                            • First post
                                              Last post