    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • gjacobseG
      gjacobse @gjacobse
      last edited by

      @gjacobse said in Pi as a UPS monitor:

      checking on my UPS this morning

      Since reboot, the monitor has been running all the time. So it may have been simply that.

      As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

      Maybe something similar to the UBNT controller software - central configuration ability.....

      1 Reply Last reply Reply Quote 0
      • travisdh1T
        travisdh1 @gjacobse
        last edited by

        @gjacobse said in Pi as a UPS monitor:

        checking on my UPS this morning

         ~ $ uptime
         09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
        
         ~ $ sudo upsc pandora
        Init SSL without certificate database
        battery.charge: 100
        battery.charge.low: 10
        battery.charge.warning: 50
        battery.date: not set
        battery.mfr.date: 2014/06/22
        battery.runtime: 3172
        battery.runtime.low: 120
        battery.type: PbAc
        battery.voltage: 13.6
        battery.voltage.nominal: 12.0
        device.mfr: APC
        device.model: Back-UPS ES 550G
        device.serial: 4B1425P54201
        device.type: ups
        driver.name: usbhid-ups
        driver.parameter.pollfreq: 30
        driver.parameter.pollinterval: 2
        driver.parameter.port: auto
        driver.version: 2.7.1
        driver.version.data: APC HID 0.95
        driver.version.internal: 0.38
        input.sensitivity: medium
        input.transfer.high: 139
        input.transfer.low: 92
        input.voltage: 126.0
        input.voltage.nominal: 120
        ups.beeper.status: enabled
        ups.delay.shutdown: 20
        ups.firmware: 904.W1 .D
        ups.firmware.aux: W1
        ups.load: 13
        ups.mfr: APC
        ups.mfr.date: 2014/06/22
        ups.model: Back-UPS ES 550G
        ups.productid: 0002
        ups.serial: 4B1425P54201
        ups.status: OL
        ups.timer.reboot: 0
        ups.timer.shutdown: -1
        ups.vendorid: 051d
        

        Since reboot, the monitor has been running all the time. So it may have been simply that.

        As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

        Take the output of upsc and throw it up on a web page. Unless you want a local display, in which case it's actually more difficult.

        1 Reply Last reply Reply Quote 0
        • thwrT
          thwr @gjacobse
          last edited by

          @gjacobse said in Pi as a UPS monitor:

          checking on my UPS this morning

           ~ $ uptime
           09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
          
           ~ $ sudo upsc pandora
          Init SSL without certificate database
          battery.charge: 100
          battery.charge.low: 10
          battery.charge.warning: 50
          battery.date: not set
          battery.mfr.date: 2014/06/22
          battery.runtime: 3172
          battery.runtime.low: 120
          battery.type: PbAc
          battery.voltage: 13.6
          battery.voltage.nominal: 12.0
          device.mfr: APC
          device.model: Back-UPS ES 550G
          device.serial: 4B1425P54201
          device.type: ups
          driver.name: usbhid-ups
          driver.parameter.pollfreq: 30
          driver.parameter.pollinterval: 2
          driver.parameter.port: auto
          driver.version: 2.7.1
          driver.version.data: APC HID 0.95
          driver.version.internal: 0.38
          input.sensitivity: medium
          input.transfer.high: 139
          input.transfer.low: 92
          input.voltage: 126.0
          input.voltage.nominal: 120
          ups.beeper.status: enabled
          ups.delay.shutdown: 20
          ups.firmware: 904.W1 .D
          ups.firmware.aux: W1
          ups.load: 13
          ups.mfr: APC
          ups.mfr.date: 2014/06/22
          ups.model: Back-UPS ES 550G
          ups.productid: 0002
          ups.serial: 4B1425P54201
          ups.status: OL
          ups.timer.reboot: 0
          ups.timer.shutdown: -1
          ups.vendorid: 051d
          

          Since reboot, the monitor has been running all the time. So it may have been simply that.

          As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

          AMQP / MQTT may be awesome for this at the transport layer. MQTT is an interesting protocol that let you define a "last will and testament" action in case something goes south.

          Ansible/Puppet etc. can handle the central configuration.

          1 Reply Last reply Reply Quote 1
          • JaredBuschJ
            JaredBusch
            last edited by

            Hey 3 months later.....

            1 Reply Last reply Reply Quote 1
            • JaredBuschJ
              JaredBusch
              last edited by

              Alright, I plugged the thing back in and got to testing.

              Yeah! It still communicates.

              pi@raspberrypi:~ $ sudo upsc jaredoffice
              Init SSL without certificate database
              battery.charge: 84
              battery.charge.low: 10
              battery.charge.warning: 50
              battery.date: 2001/09/25
              battery.mfr.date: 2010/12/15
              battery.runtime: 1236
              battery.runtime.low: 120
              battery.type: PbAc
              battery.voltage: 27.0
              battery.voltage.nominal: 24.0
              device.mfr: American Power Conversion
              device.model: Back-UPS BR1000G
              device.serial: 3B1051X20329
              device.type: ups
              driver.name: usbhid-ups
              driver.parameter.pollfreq: 30
              driver.parameter.pollinterval: 2
              driver.parameter.port: auto
              driver.version: 2.7.2
              driver.version.data: APC HID 0.95
              driver.version.internal: 0.38
              input.sensitivity: medium
              input.transfer.high: 147
              input.transfer.low: 88
              input.transfer.reason: input voltage out of range
              input.voltage: 124.0
              input.voltage.nominal: 120
              ups.beeper.status: enabled
              ups.delay.shutdown: 20
              ups.firmware: 868.L1 .D
              ups.firmware.aux: L1
              ups.load: 20
              ups.mfr: American Power Conversion
              ups.mfr.date: 2010/12/15
              ups.model: Back-UPS BR1000G
              ups.productid: 0002
              ups.realpower.nominal: 600
              ups.serial: 3B1051X20329
              ups.status: OL CHRG
              ups.test.result: No test initiated
              ups.timer.reboot: 0
              ups.timer.shutdown: -1
              ups.vendorid: 051d
              
              1 Reply Last reply Reply Quote 3
              • JaredBuschJ
                JaredBusch
                last edited by JaredBusch

                Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                Ok back to the manual and checking the conf files.

                Well it would probably help if I told the thing what to monitor..
                /etc/nut/upsmon.conf

                MONITOR jaredoffice@localhost 1 upsmon demo master
                

                Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                # put at end of file
                [upsmon]
                password = demo
                upsmon master
                

                Now reload the monitor

                pi@raspberrypi:~ $ sudo upsmon -c reload
                Network UPS Tools upsmon 2.7.2
                pi@raspberrypi:~ $
                

                Then unplug the UPS. and get nothing.

                look in the logs..
                tail/var/log/syslog

                Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                

                Say to yourself, WTF did I do 3 months ago....

                Time to reload and start over.

                gjacobseG 1 Reply Last reply Reply Quote 0
                • gjacobseG
                  gjacobse @JaredBusch
                  last edited by

                  @JaredBusch said in Pi as a UPS monitor:

                  Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                  Ok back to the manual and checking the conf files.

                  Well it would probably help if I told the thing what to monitor..
                  /etc/nut/upsmon.conf

                  MONITOR jaredoffice@localhost 1 upsmon demo master
                  

                  Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                  pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                  # put at end of file
                  [upsmon]
                  password = demo
                  upsmon master
                  

                  Now reload the monitor

                  pi@raspberrypi:~ $ sudo upsmon -c reload
                  Network UPS Tools upsmon 2.7.2
                  pi@raspberrypi:~ $
                  

                  Then unplug the UPS. and get nothing.

                  look in the logs..
                  tail/var/log/syslog

                  Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                  Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                  Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                  Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                  Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                  

                  Say to yourself, WTF did I do 3 months ago....

                  Time to reload and start over.

                  think i got the same thing, and decide the same course of action, to which I have not moved forward with. Albeit, it's not on a rPi but a desktop - premise is the same.

                  Think we may have to create a user for the NUT system.... but again,.. can't work with it right now.

                  1 Reply Last reply Reply Quote 0
                  • JaredBuschJ
                    JaredBusch
                    last edited by JaredBusch

                    Quick check of upsmon.conf found this, uncommented it.

                    # RUN_AS_USER nut
                    

                    Rebooted Pi, unplugged UPS.

                    Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:04 2017):
                    
                    UPS jaredoffice@localhost on battery
                    
                    
                    Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:24 2017):
                    
                    UPS jaredoffice@localhost on line power
                    
                    1 Reply Last reply Reply Quote 0
                    • JaredBuschJ
                      JaredBusch
                      last edited by

                      Syslog had this though.

                      Feb  1 17:19:04 raspberrypi upsmon[734]: UPS jaredoffice@localhost on battery
                      Feb  1 17:19:11 raspberrypi upssched[792]: Failed to connect to parent and failed to create parent: No such file or directory
                      Feb  1 17:19:24 raspberrypi upsmon[734]: UPS jaredoffice@localhost on line power
                      

                      Back to the config files we go!
                      /etc/nut/upssched.conf

                      # PIPEFN <filename>
                      # This is commented out by default to make you visit this file and think
                      # about how your system works before potentially opening a hole.
                      

                      FFS, but it gets better! Right below that, also commented out.

                      # LOCKFN <filename>
                      #
                      # REQUIRED.  This was added after version 1.2.1.
                      #
                      # upssched needs to be able to create this filename in order to avoid
                      # a race condition when two events are dispatched from upsmon at nearly
                      # the same time.  This file will only exist briefly.  It must not be
                      # created by any other process.
                      #
                      # You should put this in the same directory as PIPEFN.
                      #
                      

                      So I update the config and make a directory forgetting to chown it from root /sigh...

                      PIPEFN /etc/nut/upssched/upssched.pipe
                      LOCKFN /etc/nut/upssched/upssched.lock
                      1 Reply Last reply Reply Quote 0
                      • JaredBuschJ
                        JaredBusch
                        last edited by JaredBusch

                        Once it was all chowned...

                        Feb  1 17:33:08 raspberrypi upssched[793]: Timer daemon started
                        Feb  1 17:33:09 raspberrypi upssched[793]: New timer: onbattwarn (30 seconds)
                        Feb  1 17:33:39 raspberrypi upssched[793]: Event: onbattwarn
                        Feb  1 17:33:54 raspberrypi upssched[793]: Timer queue empty, exiting
                        

                        And output to the screen:

                        Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:33:39 2017):
                        
                        The UPS is currently running on battery power!
                        
                        1 Reply Last reply Reply Quote 0
                        • JaredBuschJ
                          JaredBusch
                          last edited by

                          Now time to wipe, replicate, test and document.

                          Then the command can be changed to send email.

                          1 Reply Last reply Reply Quote 3
                          • JaredBuschJ
                            JaredBusch
                            last edited by JaredBusch

                            Following my own notes from post 62
                            At step 11 (installing nut form repo) I see an error.
                            May or may not have gotten this the first time around..

                            pi@bna-pwr-pi-01:~ $ sudo apt-get install nut
                            Reading package lists... Done
                            <snip>
                            Unpacking nut (2.7.2-4) ...
                            Processing triggers for man-db (2.7.0.2-5) ...
                            Processing triggers for systemd (215-17+deb8u6) ...
                            Setting up libnspr4:armhf (2:4.12-1+debu8u1) ...
                            Setting up libnss3:armhf (2:3.26-1+debu8u1) ...
                            Setting up libupsclient4:armhf (2.7.2-4) ...
                            Setting up nut-client (2.7.2-4) ...
                            Job for nut-monitor.service failed. See 'systemctl status nut-monitor.service' and 'journalctl -xn' for details.
                            invoke-rc.d: initscript nut-client, action "start" failed.
                            Setting up nut-server (2.7.2-4) ...
                            A dependency job for nut-server.service failed. See 'journalctl -xn' for details.
                            invoke-rc.d: initscript nut-server, action "start" failed.
                            Job for nut-driver.service failed. See 'systemctl status nut-driver.service' and 'journalctl -xn' for details.
                            Setting up nut (2.7.2-4) ...
                            Processing triggers for libc-bin (2.19-18+deb8u7) ...
                            Processing triggers for systemd (215-17+deb8u6) ...
                            pi@bna-pwr-pi-01:~ $ systemctl status nut-monitor
                            ● nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller
                               Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled)
                               Active: failed (Result: resources) since Thu 2017-02-02 02:10:27 UTC; 49s ago
                            pi@bna-pwr-pi-01:~ $ 
                            
                            1 Reply Last reply Reply Quote 0
                            • JaredBuschJ
                              JaredBusch
                              last edited by

                              ah here we go, this is normal because not configured.

                              pi@bna-pwr-pi-01:~ $ sudo journalctl -xn
                              -- Logs begin at Fri 2016-11-25 18:24:08 UTC, end at Thu 2017-02-02 02:33:03 UTC. --
                              Feb 02 02:32:47 bna-pwr-pi-01 sudo[23103]: pam_unix(sudo:session): session opened for user root by pi(uid=0)
                              Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Starting Network UPS Tools - power device monitor and shutdown controller...
                              -- Subject: Unit nut-monitor.service has begun with start-up
                              -- Defined-By: systemd
                              -- Support: http://lists.freedesktop.org/mailman/listinfo/systemd-devel
                              -- 
                              -- Unit nut-monitor.service has begun starting up.
                              Feb 02 02:32:47 bna-pwr-pi-01 upsmon[23113]: upsmon disabled, please adjust the configuration to your needs
                              Feb 02 02:32:47 bna-pwr-pi-01 upsmon[23113]: Then set MODE to a suitable value in /etc/nut/nut.conf to enable it
                              Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: PID file /var/run/nut/upsmon.pid not readable (yet?) after start.
                              Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Failed to start Network UPS Tools - power device monitor and shutdown controller.
                              -- Subject: Unit nut-monitor.service has failed
                              -- Defined-By: systemd
                              -- Support: http://lists.freedesktop.org/mailman/listinfo/systemd-devel
                              -- 
                              -- Unit nut-monitor.service has failed.
                              -- 
                              -- The result is failed.
                              Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Unit nut-monitor.service entered failed state.
                              Feb 02 02:32:48 bna-pwr-pi-01 sudo[23103]: pam_unix(sudo:session): session closed for user root
                              Feb 02 02:33:03 bna-pwr-pi-01 sudo[23121]: pi : TTY=pts/0 ; PWD=/home/pi ; USER=root ; COMMAND=/bin/journalctl -xn
                              Feb 02 02:33:03 bna-pwr-pi-01 sudo[23121]: pam_unix(sudo:session): session opened for user root by pi(uid=0)
                              
                              1 Reply Last reply Reply Quote 1
                              • JaredBuschJ
                                JaredBusch
                                last edited by JaredBusch

                                So on to configuration. Nut has only a few config files you need to deal with.

                                We will go right down the list.

                                pi@bna-pwr-pi-01:~ $ ls -l /etc/nut
                                total 44
                                -rw-r----- 1 root nut  1538 Mar 26  2015 nut.conf
                                -rw-r----- 1 root nut  4572 Mar 26  2015 ups.conf
                                -rw-r----- 1 root nut  4578 Mar 26  2015 upsd.conf
                                -rw-r----- 1 root nut  2131 Mar 26  2015 upsd.users
                                -rw-r----- 1 root nut 15170 Mar 26  2015 upsmon.conf
                                -rw-r----- 1 root nut  3887 Mar 26  2015 upssched.conf
                                
                                1 Reply Last reply Reply Quote 0
                                • JaredBuschJ
                                  JaredBusch
                                  last edited by

                                  First up is nut.conf. There is only a single option to set in this file, but it is important.

                                  Assuming you are going to have only one device, or if multiple devices, that they will report in on their own, the simplest configuration is to choose standalone

                                  MODE=standalone
                                  

                                  Here are the various meanings from the conf file.

                                  # - none: NUT is not configured, or use the Integrated Power Management, or use
                                  #   some external system to startup NUT components. So nothing is to be started.
                                  # - standalone: This mode address a local only configuration, with 1 UPS
                                  #   protecting the local system. This implies to start the 3 NUT layers (driver,
                                  #   upsd and upsmon) and the matching configuration files. This mode can also
                                  #   address UPS redundancy.
                                  # - netserver: same as for the standalone configuration, but also need
                                  #   some more network access controls (firewall, tcp-wrappers) and possibly a
                                  #   specific LISTEN directive in upsd.conf.
                                  #   Since this MODE is opened to the network, a special care should be applied
                                  #   to security concerns.
                                  # - netclient: this mode only requires upsmon.
                                  
                                  1 Reply Last reply Reply Quote 0
                                  • JaredBuschJ
                                    JaredBusch
                                    last edited by

                                    Next up is ups.conf, again read the config file for more information, it is fairly thorough.

                                    In this case I am going to connect it to the APC unit pictured at the beginning of this thread.

                                    [bnajaredrouter]
                                    driver = usbhid-ups
                                    port = auto
                                    desc = "Jared Router UPS"
                                    
                                    1 Reply Last reply Reply Quote 0
                                    • JaredBuschJ
                                      JaredBusch
                                      last edited by

                                      The file upsd.conf does not need modified for a typical standalone setup.

                                      1 Reply Last reply Reply Quote 0
                                      • JaredBuschJ
                                        JaredBusch
                                        last edited by

                                        The file upsd.users needs modified to have the authentication that upsmon will use added to the end of the file.

                                        [bnaupsmon]
                                        password = AGoodPassword
                                        upsmon master
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • JaredBuschJ
                                          JaredBusch
                                          last edited by

                                          The file upsmon.conf starts to get into the nuts and bolts of setting things up to do things for you.

                                          First up will be to uncomment the run as user setting.

                                          RUN_AS_USER nut
                                          

                                          Next is creating the monitor line to tell it what system to monitor. This uses the settings from ups.conf and upsd.users that you previously configured.

                                          MONITOR bnajaredrouter@localhost 1 bnaupsmon AGoodPassword master
                                          

                                          continuing down the file, the next thing to do is to set notifycmd to point to the upssched program

                                          NOTIFYCMD /sbin/upssched
                                          

                                          The final part of this file is to uncomment all of the notify flags and add the EXEC flag to the ones you want to fire the above upssched application. Leaving WALL in while testing is useful, but pretty pointless later for me since the goal is a remote alert.

                                          NOTIFYFLAG ONLINE       SYSLOG+WALL+EXEC
                                          NOTIFYFLAG ONBATT       SYSLOG+WALL+EXEC
                                          NOTIFYFLAG LOWBATT      SYSLOG+WALL
                                          NOTIFYFLAG FSD          SYSLOG+WALL
                                          NOTIFYFLAG COMMOK       SYSLOG+WALL
                                          NOTIFYFLAG COMMBAD      SYSLOG+WALL
                                          NOTIFYFLAG SHUTDOWN     SYSLOG+WALL
                                          NOTIFYFLAG REPLBATT     SYSLOG+WALL
                                          NOTIFYFLAG NOCOMM       SYSLOG+WALL
                                          NOTIFYFLAG NOPARENT     SYSLOG+WALL
                                          
                                          1 Reply Last reply Reply Quote 0
                                          • JaredBuschJ
                                            JaredBusch
                                            last edited by JaredBusch

                                            If you never set any of the flags to EXEC in the previous section, there is nothing to do here, you can stop. But what would be the point of a remote alerting device that does not alert.

                                            So now we come to the last conf file upssched.conf. This one is a bit more annoying because the developers intentionally chose to ship this broken to 'force' you to set up a file yourself.
                                            By default, PIPEFN and LOCKFN are commented out and point to the /var/run/nut/upssched directory that does not exist.

                                            # PIPEFN /var/run/nut/upssched/upssched.pipe
                                            # LOCKFN /var/run/nut/upssched/upssched.lock
                                            

                                            So we make a directory and the pipe file. You are instructed to not make the lock file in the comments.

                                            sudo mkdir /etc/nut/upssched
                                            sudo chown nut:nut /etc/nut/upssched
                                            sudo touch /etc/nut/upssched/upssched.pipe
                                            sudo chown nut:nut /etc/nut/upssched/upssched.pipe
                                            

                                            Editing this file, note the location the shell script that will be called. This is the default, and there is an example script already there, ready to be modified.

                                            CMDSCRIPT /bin/upssched-cmd
                                            

                                            Uncomment and update the PIPE and LOCK lines.

                                            PIPEFN /etc/nut/upssched/upssched.pipe
                                            LOCKFN /etc/nut/upssched/upssched.lock
                                            

                                            Now comes the part that does work, the AT commads. You will want to read the comments and likely the documentation to make full use of this. But here are a couple examples of AT commands to get you going.
                                            When the unit goes on battery, call the shell script to start a 30 second timer named 'onbattwarn'. When the power comes back online, cancel the timer.

                                            AT ONBATT * START-TIMER onbattwarn 30
                                            AT ONLINE * CANCEL-TIMER onbattwarn
                                            AT ONLINE * EXECUTE ongrid
                                            
                                            1 Reply Last reply Reply Quote 0