    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • gjacobseG
      gjacobse
      last edited by

      checking on my UPS this morning

       ~ $ uptime
       09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
      
       ~ $ sudo upsc pandora
      Init SSL without certificate database
      battery.charge: 100
      battery.charge.low: 10
      battery.charge.warning: 50
      battery.date: not set
      battery.mfr.date: 2014/06/22
      battery.runtime: 3172
      battery.runtime.low: 120
      battery.type: PbAc
      battery.voltage: 13.6
      battery.voltage.nominal: 12.0
      device.mfr: APC
      device.model: Back-UPS ES 550G
      device.serial: 4B1425P54201
      device.type: ups
      driver.name: usbhid-ups
      driver.parameter.pollfreq: 30
      driver.parameter.pollinterval: 2
      driver.parameter.port: auto
      driver.version: 2.7.1
      driver.version.data: APC HID 0.95
      driver.version.internal: 0.38
      input.sensitivity: medium
      input.transfer.high: 139
      input.transfer.low: 92
      input.voltage: 126.0
      input.voltage.nominal: 120
      ups.beeper.status: enabled
      ups.delay.shutdown: 20
      ups.firmware: 904.W1 .D
      ups.firmware.aux: W1
      ups.load: 13
      ups.mfr: APC
      ups.mfr.date: 2014/06/22
      ups.model: Back-UPS ES 550G
      ups.productid: 0002
      ups.serial: 4B1425P54201
      ups.status: OL
      ups.timer.reboot: 0
      ups.timer.shutdown: -1
      ups.vendorid: 051d
      

      Since reboot, the monitor has been running all the time. So it may have been simply that.

      As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

      gjacobseG travisdh1T thwrT 3 Replies Last reply Reply Quote 1
      • gjacobseG
        gjacobse @gjacobse
        last edited by

        @gjacobse said in Pi as a UPS monitor:

        checking on my UPS this morning

        Since reboot, the monitor has been running all the time. So it may have been simply that.

        As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

        Maybe something similar to the UBNT controller software - central configuration ability.....

        1 Reply Last reply Reply Quote 0
        • travisdh1T
          travisdh1 @gjacobse
          last edited by

          @gjacobse said in Pi as a UPS monitor:

          checking on my UPS this morning

           ~ $ uptime
           09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
          
           ~ $ sudo upsc pandora
          Init SSL without certificate database
          battery.charge: 100
          battery.charge.low: 10
          battery.charge.warning: 50
          battery.date: not set
          battery.mfr.date: 2014/06/22
          battery.runtime: 3172
          battery.runtime.low: 120
          battery.type: PbAc
          battery.voltage: 13.6
          battery.voltage.nominal: 12.0
          device.mfr: APC
          device.model: Back-UPS ES 550G
          device.serial: 4B1425P54201
          device.type: ups
          driver.name: usbhid-ups
          driver.parameter.pollfreq: 30
          driver.parameter.pollinterval: 2
          driver.parameter.port: auto
          driver.version: 2.7.1
          driver.version.data: APC HID 0.95
          driver.version.internal: 0.38
          input.sensitivity: medium
          input.transfer.high: 139
          input.transfer.low: 92
          input.voltage: 126.0
          input.voltage.nominal: 120
          ups.beeper.status: enabled
          ups.delay.shutdown: 20
          ups.firmware: 904.W1 .D
          ups.firmware.aux: W1
          ups.load: 13
          ups.mfr: APC
          ups.mfr.date: 2014/06/22
          ups.model: Back-UPS ES 550G
          ups.productid: 0002
          ups.serial: 4B1425P54201
          ups.status: OL
          ups.timer.reboot: 0
          ups.timer.shutdown: -1
          ups.vendorid: 051d
          

          Since reboot, the monitor has been running all the time. So it may have been simply that.

          As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

          Take the output of upsc and throw it up on a web page. Unless you want a local display, in which case it's actually more difficult.

          1 Reply Last reply Reply Quote 0
          • thwrT
            thwr @gjacobse
            last edited by

            @gjacobse said in Pi as a UPS monitor:

            checking on my UPS this morning

             ~ $ uptime
             09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
            
             ~ $ sudo upsc pandora
            Init SSL without certificate database
            battery.charge: 100
            battery.charge.low: 10
            battery.charge.warning: 50
            battery.date: not set
            battery.mfr.date: 2014/06/22
            battery.runtime: 3172
            battery.runtime.low: 120
            battery.type: PbAc
            battery.voltage: 13.6
            battery.voltage.nominal: 12.0
            device.mfr: APC
            device.model: Back-UPS ES 550G
            device.serial: 4B1425P54201
            device.type: ups
            driver.name: usbhid-ups
            driver.parameter.pollfreq: 30
            driver.parameter.pollinterval: 2
            driver.parameter.port: auto
            driver.version: 2.7.1
            driver.version.data: APC HID 0.95
            driver.version.internal: 0.38
            input.sensitivity: medium
            input.transfer.high: 139
            input.transfer.low: 92
            input.voltage: 126.0
            input.voltage.nominal: 120
            ups.beeper.status: enabled
            ups.delay.shutdown: 20
            ups.firmware: 904.W1 .D
            ups.firmware.aux: W1
            ups.load: 13
            ups.mfr: APC
            ups.mfr.date: 2014/06/22
            ups.model: Back-UPS ES 550G
            ups.productid: 0002
            ups.serial: 4B1425P54201
            ups.status: OL
            ups.timer.reboot: 0
            ups.timer.shutdown: -1
            ups.vendorid: 051d
            

            Since reboot, the monitor has been running all the time. So it may have been simply that.

            As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

            AMQP / MQTT may be awesome for this at the transport layer. MQTT is an interesting protocol that let you define a "last will and testament" action in case something goes south.

            Ansible/Puppet etc. can handle the central configuration.

            1 Reply Last reply Reply Quote 1
            • JaredBuschJ
              JaredBusch
              last edited by

              Hey 3 months later.....

              1 Reply Last reply Reply Quote 1
              • JaredBuschJ
                JaredBusch
                last edited by

                Alright, I plugged the thing back in and got to testing.

                Yeah! It still communicates.

                pi@raspberrypi:~ $ sudo upsc jaredoffice
                Init SSL without certificate database
                battery.charge: 84
                battery.charge.low: 10
                battery.charge.warning: 50
                battery.date: 2001/09/25
                battery.mfr.date: 2010/12/15
                battery.runtime: 1236
                battery.runtime.low: 120
                battery.type: PbAc
                battery.voltage: 27.0
                battery.voltage.nominal: 24.0
                device.mfr: American Power Conversion
                device.model: Back-UPS BR1000G
                device.serial: 3B1051X20329
                device.type: ups
                driver.name: usbhid-ups
                driver.parameter.pollfreq: 30
                driver.parameter.pollinterval: 2
                driver.parameter.port: auto
                driver.version: 2.7.2
                driver.version.data: APC HID 0.95
                driver.version.internal: 0.38
                input.sensitivity: medium
                input.transfer.high: 147
                input.transfer.low: 88
                input.transfer.reason: input voltage out of range
                input.voltage: 124.0
                input.voltage.nominal: 120
                ups.beeper.status: enabled
                ups.delay.shutdown: 20
                ups.firmware: 868.L1 .D
                ups.firmware.aux: L1
                ups.load: 20
                ups.mfr: American Power Conversion
                ups.mfr.date: 2010/12/15
                ups.model: Back-UPS BR1000G
                ups.productid: 0002
                ups.realpower.nominal: 600
                ups.serial: 3B1051X20329
                ups.status: OL CHRG
                ups.test.result: No test initiated
                ups.timer.reboot: 0
                ups.timer.shutdown: -1
                ups.vendorid: 051d
                
                1 Reply Last reply Reply Quote 3
                • JaredBuschJ
                  JaredBusch
                  last edited by JaredBusch

                  Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                  Ok back to the manual and checking the conf files.

                  Well it would probably help if I told the thing what to monitor..
                  /etc/nut/upsmon.conf

                  MONITOR jaredoffice@localhost 1 upsmon demo master
                  

                  Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                  pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                  # put at end of file
                  [upsmon]
                  password = demo
                  upsmon master
                  

                  Now reload the monitor

                  pi@raspberrypi:~ $ sudo upsmon -c reload
                  Network UPS Tools upsmon 2.7.2
                  pi@raspberrypi:~ $
                  

                  Then unplug the UPS. and get nothing.

                  look in the logs..
                  tail/var/log/syslog

                  Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                  Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                  Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                  Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                  Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                  

                  Say to yourself, WTF did I do 3 months ago....

                  Time to reload and start over.

                  gjacobseG 1 Reply Last reply Reply Quote 0
                  • gjacobseG
                    gjacobse @JaredBusch
                    last edited by

                    @JaredBusch said in Pi as a UPS monitor:

                    Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                    Ok back to the manual and checking the conf files.

                    Well it would probably help if I told the thing what to monitor..
                    /etc/nut/upsmon.conf

                    MONITOR jaredoffice@localhost 1 upsmon demo master
                    

                    Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                    pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                    # put at end of file
                    [upsmon]
                    password = demo
                    upsmon master
                    

                    Now reload the monitor

                    pi@raspberrypi:~ $ sudo upsmon -c reload
                    Network UPS Tools upsmon 2.7.2
                    pi@raspberrypi:~ $
                    

                    Then unplug the UPS. and get nothing.

                    look in the logs..
                    tail/var/log/syslog

                    Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                    Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                    Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                    Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                    Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                    

                    Say to yourself, WTF did I do 3 months ago....

                    Time to reload and start over.

                    think i got the same thing, and decide the same course of action, to which I have not moved forward with. Albeit, it's not on a rPi but a desktop - premise is the same.

                    Think we may have to create a user for the NUT system.... but again,.. can't work with it right now.

                    1 Reply Last reply Reply Quote 0
                    • JaredBuschJ
                      JaredBusch
                      last edited by JaredBusch

                      Quick check of upsmon.conf found this, uncommented it.

                      # RUN_AS_USER nut
                      

                      Rebooted Pi, unplugged UPS.

                      Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:04 2017):
                      
                      UPS jaredoffice@localhost on battery
                      
                      
                      Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:24 2017):
                      
                      UPS jaredoffice@localhost on line power
                      
                      1 Reply Last reply Reply Quote 0
                      • JaredBuschJ
                        JaredBusch
                        last edited by

                        Syslog had this though.

                        Feb  1 17:19:04 raspberrypi upsmon[734]: UPS jaredoffice@localhost on battery
                        Feb  1 17:19:11 raspberrypi upssched[792]: Failed to connect to parent and failed to create parent: No such file or directory
                        Feb  1 17:19:24 raspberrypi upsmon[734]: UPS jaredoffice@localhost on line power
                        

                        Back to the config files we go!
                        /etc/nut/upssched.conf

                        # PIPEFN <filename>
                        # This is commented out by default to make you visit this file and think
                        # about how your system works before potentially opening a hole.
                        

                        FFS, but it gets better! Right below that, also commented out.

                        # LOCKFN <filename>
                        #
                        # REQUIRED.  This was added after version 1.2.1.
                        #
                        # upssched needs to be able to create this filename in order to avoid
                        # a race condition when two events are dispatched from upsmon at nearly
                        # the same time.  This file will only exist briefly.  It must not be
                        # created by any other process.
                        #
                        # You should put this in the same directory as PIPEFN.
                        #
                        

                        So I update the config and make a directory forgetting to chown it from root /sigh...

                        PIPEFN /etc/nut/upssched/upssched.pipe
                        LOCKFN /etc/nut/upssched/upssched.lock
                        1 Reply Last reply Reply Quote 0
                        • JaredBuschJ
                          JaredBusch
                          last edited by JaredBusch

                          Once it was all chowned...

                          Feb  1 17:33:08 raspberrypi upssched[793]: Timer daemon started
                          Feb  1 17:33:09 raspberrypi upssched[793]: New timer: onbattwarn (30 seconds)
                          Feb  1 17:33:39 raspberrypi upssched[793]: Event: onbattwarn
                          Feb  1 17:33:54 raspberrypi upssched[793]: Timer queue empty, exiting
                          

                          And output to the screen:

                          Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:33:39 2017):
                          
                          The UPS is currently running on battery power!
                          
                          1 Reply Last reply Reply Quote 0
                          • JaredBuschJ
                            JaredBusch
                            last edited by

                            Now time to wipe, replicate, test and document.

                            Then the command can be changed to send email.

                            1 Reply Last reply Reply Quote 3
                            • JaredBuschJ
                              JaredBusch
                              last edited by JaredBusch

                              Following my own notes from post 62
                              At step 11 (installing nut form repo) I see an error.
                              May or may not have gotten this the first time around..

                              pi@bna-pwr-pi-01:~ $ sudo apt-get install nut
                              Reading package lists... Done
                              <snip>
                              Unpacking nut (2.7.2-4) ...
                              Processing triggers for man-db (2.7.0.2-5) ...
                              Processing triggers for systemd (215-17+deb8u6) ...
                              Setting up libnspr4:armhf (2:4.12-1+debu8u1) ...
                              Setting up libnss3:armhf (2:3.26-1+debu8u1) ...
                              Setting up libupsclient4:armhf (2.7.2-4) ...
                              Setting up nut-client (2.7.2-4) ...
                              Job for nut-monitor.service failed. See 'systemctl status nut-monitor.service' and 'journalctl -xn' for details.
                              invoke-rc.d: initscript nut-client, action "start" failed.
                              Setting up nut-server (2.7.2-4) ...
                              A dependency job for nut-server.service failed. See 'journalctl -xn' for details.
                              invoke-rc.d: initscript nut-server, action "start" failed.
                              Job for nut-driver.service failed. See 'systemctl status nut-driver.service' and 'journalctl -xn' for details.
                              Setting up nut (2.7.2-4) ...
                              Processing triggers for libc-bin (2.19-18+deb8u7) ...
                              Processing triggers for systemd (215-17+deb8u6) ...
                              pi@bna-pwr-pi-01:~ $ systemctl status nut-monitor
                              ● nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller
                                 Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled)
                                 Active: failed (Result: resources) since Thu 2017-02-02 02:10:27 UTC; 49s ago
                              pi@bna-pwr-pi-01:~ $ 
                              
                              1 Reply Last reply Reply Quote 0
                              • JaredBuschJ
                                JaredBusch
                                last edited by

                                ah here we go, this is normal because not configured.

                                pi@bna-pwr-pi-01:~ $ sudo journalctl -xn
                                -- Logs begin at Fri 2016-11-25 18:24:08 UTC, end at Thu 2017-02-02 02:33:03 UTC. --
                                Feb 02 02:32:47 bna-pwr-pi-01 sudo[23103]: pam_unix(sudo:session): session opened for user root by pi(uid=0)
                                Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Starting Network UPS Tools - power device monitor and shutdown controller...
                                -- Subject: Unit nut-monitor.service has begun with start-up
                                -- Defined-By: systemd
                                -- Support: http://lists.freedesktop.org/mailman/listinfo/systemd-devel
                                -- 
                                -- Unit nut-monitor.service has begun starting up.
                                Feb 02 02:32:47 bna-pwr-pi-01 upsmon[23113]: upsmon disabled, please adjust the configuration to your needs
                                Feb 02 02:32:47 bna-pwr-pi-01 upsmon[23113]: Then set MODE to a suitable value in /etc/nut/nut.conf to enable it
                                Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: PID file /var/run/nut/upsmon.pid not readable (yet?) after start.
                                Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Failed to start Network UPS Tools - power device monitor and shutdown controller.
                                -- Subject: Unit nut-monitor.service has failed
                                -- Defined-By: systemd
                                -- Support: http://lists.freedesktop.org/mailman/listinfo/systemd-devel
                                -- 
                                -- Unit nut-monitor.service has failed.
                                -- 
                                -- The result is failed.
                                Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Unit nut-monitor.service entered failed state.
                                Feb 02 02:32:48 bna-pwr-pi-01 sudo[23103]: pam_unix(sudo:session): session closed for user root
                                Feb 02 02:33:03 bna-pwr-pi-01 sudo[23121]: pi : TTY=pts/0 ; PWD=/home/pi ; USER=root ; COMMAND=/bin/journalctl -xn
                                Feb 02 02:33:03 bna-pwr-pi-01 sudo[23121]: pam_unix(sudo:session): session opened for user root by pi(uid=0)
                                
                                1 Reply Last reply Reply Quote 1
                                • JaredBuschJ
                                  JaredBusch
                                  last edited by JaredBusch

                                  So on to configuration. Nut has only a few config files you need to deal with.

                                  We will go right down the list.

                                  pi@bna-pwr-pi-01:~ $ ls -l /etc/nut
                                  total 44
                                  -rw-r----- 1 root nut  1538 Mar 26  2015 nut.conf
                                  -rw-r----- 1 root nut  4572 Mar 26  2015 ups.conf
                                  -rw-r----- 1 root nut  4578 Mar 26  2015 upsd.conf
                                  -rw-r----- 1 root nut  2131 Mar 26  2015 upsd.users
                                  -rw-r----- 1 root nut 15170 Mar 26  2015 upsmon.conf
                                  -rw-r----- 1 root nut  3887 Mar 26  2015 upssched.conf
                                  
                                  1 Reply Last reply Reply Quote 0
                                  • JaredBuschJ
                                    JaredBusch
                                    last edited by

                                    First up is nut.conf. There is only a single option to set in this file, but it is important.

                                    Assuming you are going to have only one device, or if multiple devices, that they will report in on their own, the simplest configuration is to choose standalone

                                    MODE=standalone
                                    

                                    Here are the various meanings from the conf file.

                                    # - none: NUT is not configured, or use the Integrated Power Management, or use
                                    #   some external system to startup NUT components. So nothing is to be started.
                                    # - standalone: This mode address a local only configuration, with 1 UPS
                                    #   protecting the local system. This implies to start the 3 NUT layers (driver,
                                    #   upsd and upsmon) and the matching configuration files. This mode can also
                                    #   address UPS redundancy.
                                    # - netserver: same as for the standalone configuration, but also need
                                    #   some more network access controls (firewall, tcp-wrappers) and possibly a
                                    #   specific LISTEN directive in upsd.conf.
                                    #   Since this MODE is opened to the network, a special care should be applied
                                    #   to security concerns.
                                    # - netclient: this mode only requires upsmon.
                                    
                                    1 Reply Last reply Reply Quote 0
                                    • JaredBuschJ
                                      JaredBusch
                                      last edited by

                                      Next up is ups.conf, again read the config file for more information, it is fairly thorough.

                                      In this case I am going to connect it to the APC unit pictured at the beginning of this thread.

                                      [bnajaredrouter]
                                      driver = usbhid-ups
                                      port = auto
                                      desc = "Jared Router UPS"
                                      
                                      1 Reply Last reply Reply Quote 0
                                      • JaredBuschJ
                                        JaredBusch
                                        last edited by

                                        The file upsd.conf does not need modified for a typical standalone setup.

                                        1 Reply Last reply Reply Quote 0
                                        • JaredBuschJ
                                          JaredBusch
                                          last edited by

                                          The file upsd.users needs modified to have the authentication that upsmon will use added to the end of the file.

                                          [bnaupsmon]
                                          password = AGoodPassword
                                          upsmon master
                                          
                                          1 Reply Last reply Reply Quote 0
                                          • JaredBuschJ
                                            JaredBusch
                                            last edited by

                                            The file upsmon.conf starts to get into the nuts and bolts of setting things up to do things for you.

                                            First up will be to uncomment the run as user setting.

                                            RUN_AS_USER nut
                                            

                                            Next is creating the monitor line to tell it what system to monitor. This uses the settings from ups.conf and upsd.users that you previously configured.

                                            MONITOR bnajaredrouter@localhost 1 bnaupsmon AGoodPassword master
                                            

                                            continuing down the file, the next thing to do is to set notifycmd to point to the upssched program

                                            NOTIFYCMD /sbin/upssched
                                            

                                            The final part of this file is to uncomment all of the notify flags and add the EXEC flag to the ones you want to fire the above upssched application. Leaving WALL in while testing is useful, but pretty pointless later for me since the goal is a remote alert.

                                            NOTIFYFLAG ONLINE       SYSLOG+WALL+EXEC
                                            NOTIFYFLAG ONBATT       SYSLOG+WALL+EXEC
                                            NOTIFYFLAG LOWBATT      SYSLOG+WALL
                                            NOTIFYFLAG FSD          SYSLOG+WALL
                                            NOTIFYFLAG COMMOK       SYSLOG+WALL
                                            NOTIFYFLAG COMMBAD      SYSLOG+WALL
                                            NOTIFYFLAG SHUTDOWN     SYSLOG+WALL
                                            NOTIFYFLAG REPLBATT     SYSLOG+WALL
                                            NOTIFYFLAG NOCOMM       SYSLOG+WALL
                                            NOTIFYFLAG NOPARENT     SYSLOG+WALL
                                            
                                            1 Reply Last reply Reply Quote 0