    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.9k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • JaredBuschJ
      JaredBusch
      last edited by

      This is what I will be following to configure reporting/alerting.
      http://www.techrepublic.com/article/customize-ups-related-alerts-in-nut/

      gjacobseG 1 Reply Last reply Reply Quote 1
      • gjacobseG
        gjacobse @JaredBusch
        last edited by

        @JaredBusch
        Well push comes to Meh -okay. I restarted the box and it's polls now.

        Won't do anything else with it for a spell to see if it retains it. It's been four days since I restarted it. Now - to reconnect to it as I had to pull the monitor off. X2Go works great,.. but only once I've signed in at the local. sure that is omething that can be changed.

        1 Reply Last reply Reply Quote 0
        • gjacobseG
          gjacobse
          last edited by

          checking on my UPS this morning

           ~ $ uptime
           09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
          
           ~ $ sudo upsc pandora
          Init SSL without certificate database
          battery.charge: 100
          battery.charge.low: 10
          battery.charge.warning: 50
          battery.date: not set
          battery.mfr.date: 2014/06/22
          battery.runtime: 3172
          battery.runtime.low: 120
          battery.type: PbAc
          battery.voltage: 13.6
          battery.voltage.nominal: 12.0
          device.mfr: APC
          device.model: Back-UPS ES 550G
          device.serial: 4B1425P54201
          device.type: ups
          driver.name: usbhid-ups
          driver.parameter.pollfreq: 30
          driver.parameter.pollinterval: 2
          driver.parameter.port: auto
          driver.version: 2.7.1
          driver.version.data: APC HID 0.95
          driver.version.internal: 0.38
          input.sensitivity: medium
          input.transfer.high: 139
          input.transfer.low: 92
          input.voltage: 126.0
          input.voltage.nominal: 120
          ups.beeper.status: enabled
          ups.delay.shutdown: 20
          ups.firmware: 904.W1 .D
          ups.firmware.aux: W1
          ups.load: 13
          ups.mfr: APC
          ups.mfr.date: 2014/06/22
          ups.model: Back-UPS ES 550G
          ups.productid: 0002
          ups.serial: 4B1425P54201
          ups.status: OL
          ups.timer.reboot: 0
          ups.timer.shutdown: -1
          ups.vendorid: 051d
          

          Since reboot, the monitor has been running all the time. So it may have been simply that.

          As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

          gjacobseG travisdh1T thwrT 3 Replies Last reply Reply Quote 1
          • gjacobseG
            gjacobse @gjacobse
            last edited by

            @gjacobse said in Pi as a UPS monitor:

            checking on my UPS this morning

            Since reboot, the monitor has been running all the time. So it may have been simply that.

            As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

            Maybe something similar to the UBNT controller software - central configuration ability.....

            1 Reply Last reply Reply Quote 0
            • travisdh1T
              travisdh1 @gjacobse
              last edited by

              @gjacobse said in Pi as a UPS monitor:

              checking on my UPS this morning

               ~ $ uptime
               09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
              
               ~ $ sudo upsc pandora
              Init SSL without certificate database
              battery.charge: 100
              battery.charge.low: 10
              battery.charge.warning: 50
              battery.date: not set
              battery.mfr.date: 2014/06/22
              battery.runtime: 3172
              battery.runtime.low: 120
              battery.type: PbAc
              battery.voltage: 13.6
              battery.voltage.nominal: 12.0
              device.mfr: APC
              device.model: Back-UPS ES 550G
              device.serial: 4B1425P54201
              device.type: ups
              driver.name: usbhid-ups
              driver.parameter.pollfreq: 30
              driver.parameter.pollinterval: 2
              driver.parameter.port: auto
              driver.version: 2.7.1
              driver.version.data: APC HID 0.95
              driver.version.internal: 0.38
              input.sensitivity: medium
              input.transfer.high: 139
              input.transfer.low: 92
              input.voltage: 126.0
              input.voltage.nominal: 120
              ups.beeper.status: enabled
              ups.delay.shutdown: 20
              ups.firmware: 904.W1 .D
              ups.firmware.aux: W1
              ups.load: 13
              ups.mfr: APC
              ups.mfr.date: 2014/06/22
              ups.model: Back-UPS ES 550G
              ups.productid: 0002
              ups.serial: 4B1425P54201
              ups.status: OL
              ups.timer.reboot: 0
              ups.timer.shutdown: -1
              ups.vendorid: 051d
              

              Since reboot, the monitor has been running all the time. So it may have been simply that.

              As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

              Take the output of upsc and throw it up on a web page. Unless you want a local display, in which case it's actually more difficult.

              1 Reply Last reply Reply Quote 0
              • thwrT
                thwr @gjacobse
                last edited by

                @gjacobse said in Pi as a UPS monitor:

                checking on my UPS this morning

                 ~ $ uptime
                 09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                
                 ~ $ sudo upsc pandora
                Init SSL without certificate database
                battery.charge: 100
                battery.charge.low: 10
                battery.charge.warning: 50
                battery.date: not set
                battery.mfr.date: 2014/06/22
                battery.runtime: 3172
                battery.runtime.low: 120
                battery.type: PbAc
                battery.voltage: 13.6
                battery.voltage.nominal: 12.0
                device.mfr: APC
                device.model: Back-UPS ES 550G
                device.serial: 4B1425P54201
                device.type: ups
                driver.name: usbhid-ups
                driver.parameter.pollfreq: 30
                driver.parameter.pollinterval: 2
                driver.parameter.port: auto
                driver.version: 2.7.1
                driver.version.data: APC HID 0.95
                driver.version.internal: 0.38
                input.sensitivity: medium
                input.transfer.high: 139
                input.transfer.low: 92
                input.voltage: 126.0
                input.voltage.nominal: 120
                ups.beeper.status: enabled
                ups.delay.shutdown: 20
                ups.firmware: 904.W1 .D
                ups.firmware.aux: W1
                ups.load: 13
                ups.mfr: APC
                ups.mfr.date: 2014/06/22
                ups.model: Back-UPS ES 550G
                ups.productid: 0002
                ups.serial: 4B1425P54201
                ups.status: OL
                ups.timer.reboot: 0
                ups.timer.shutdown: -1
                ups.vendorid: 051d
                

                Since reboot, the monitor has been running all the time. So it may have been simply that.

                As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                AMQP / MQTT may be awesome for this at the transport layer. MQTT is an interesting protocol that let you define a "last will and testament" action in case something goes south.

                Ansible/Puppet etc. can handle the central configuration.

                1 Reply Last reply Reply Quote 1
                • JaredBuschJ
                  JaredBusch
                  last edited by

                  Hey 3 months later.....

                  1 Reply Last reply Reply Quote 1
                  • JaredBuschJ
                    JaredBusch
                    last edited by

                    Alright, I plugged the thing back in and got to testing.

                    Yeah! It still communicates.

                    pi@raspberrypi:~ $ sudo upsc jaredoffice
                    Init SSL without certificate database
                    battery.charge: 84
                    battery.charge.low: 10
                    battery.charge.warning: 50
                    battery.date: 2001/09/25
                    battery.mfr.date: 2010/12/15
                    battery.runtime: 1236
                    battery.runtime.low: 120
                    battery.type: PbAc
                    battery.voltage: 27.0
                    battery.voltage.nominal: 24.0
                    device.mfr: American Power Conversion
                    device.model: Back-UPS BR1000G
                    device.serial: 3B1051X20329
                    device.type: ups
                    driver.name: usbhid-ups
                    driver.parameter.pollfreq: 30
                    driver.parameter.pollinterval: 2
                    driver.parameter.port: auto
                    driver.version: 2.7.2
                    driver.version.data: APC HID 0.95
                    driver.version.internal: 0.38
                    input.sensitivity: medium
                    input.transfer.high: 147
                    input.transfer.low: 88
                    input.transfer.reason: input voltage out of range
                    input.voltage: 124.0
                    input.voltage.nominal: 120
                    ups.beeper.status: enabled
                    ups.delay.shutdown: 20
                    ups.firmware: 868.L1 .D
                    ups.firmware.aux: L1
                    ups.load: 20
                    ups.mfr: American Power Conversion
                    ups.mfr.date: 2010/12/15
                    ups.model: Back-UPS BR1000G
                    ups.productid: 0002
                    ups.realpower.nominal: 600
                    ups.serial: 3B1051X20329
                    ups.status: OL CHRG
                    ups.test.result: No test initiated
                    ups.timer.reboot: 0
                    ups.timer.shutdown: -1
                    ups.vendorid: 051d
                    
                    1 Reply Last reply Reply Quote 3
                    • JaredBuschJ
                      JaredBusch
                      last edited by JaredBusch

                      Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                      Ok back to the manual and checking the conf files.

                      Well it would probably help if I told the thing what to monitor..
                      /etc/nut/upsmon.conf

                      MONITOR jaredoffice@localhost 1 upsmon demo master
                      

                      Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                      pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                      # put at end of file
                      [upsmon]
                      password = demo
                      upsmon master
                      

                      Now reload the monitor

                      pi@raspberrypi:~ $ sudo upsmon -c reload
                      Network UPS Tools upsmon 2.7.2
                      pi@raspberrypi:~ $
                      

                      Then unplug the UPS. and get nothing.

                      look in the logs..
                      tail/var/log/syslog

                      Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                      Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                      Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                      Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                      Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                      

                      Say to yourself, WTF did I do 3 months ago....

                      Time to reload and start over.

                      gjacobseG 1 Reply Last reply Reply Quote 0
                      • gjacobseG
                        gjacobse @JaredBusch
                        last edited by

                        @JaredBusch said in Pi as a UPS monitor:

                        Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                        Ok back to the manual and checking the conf files.

                        Well it would probably help if I told the thing what to monitor..
                        /etc/nut/upsmon.conf

                        MONITOR jaredoffice@localhost 1 upsmon demo master
                        

                        Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                        pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                        # put at end of file
                        [upsmon]
                        password = demo
                        upsmon master
                        

                        Now reload the monitor

                        pi@raspberrypi:~ $ sudo upsmon -c reload
                        Network UPS Tools upsmon 2.7.2
                        pi@raspberrypi:~ $
                        

                        Then unplug the UPS. and get nothing.

                        look in the logs..
                        tail/var/log/syslog

                        Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                        Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                        Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                        Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                        Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                        

                        Say to yourself, WTF did I do 3 months ago....

                        Time to reload and start over.

                        think i got the same thing, and decide the same course of action, to which I have not moved forward with. Albeit, it's not on a rPi but a desktop - premise is the same.

                        Think we may have to create a user for the NUT system.... but again,.. can't work with it right now.

                        1 Reply Last reply Reply Quote 0
                        • JaredBuschJ
                          JaredBusch
                          last edited by JaredBusch

                          Quick check of upsmon.conf found this, uncommented it.

                          # RUN_AS_USER nut
                          

                          Rebooted Pi, unplugged UPS.

                          Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:04 2017):
                          
                          UPS jaredoffice@localhost on battery
                          
                          
                          Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:24 2017):
                          
                          UPS jaredoffice@localhost on line power
                          
                          1 Reply Last reply Reply Quote 0
                          • JaredBuschJ
                            JaredBusch
                            last edited by

                            Syslog had this though.

                            Feb  1 17:19:04 raspberrypi upsmon[734]: UPS jaredoffice@localhost on battery
                            Feb  1 17:19:11 raspberrypi upssched[792]: Failed to connect to parent and failed to create parent: No such file or directory
                            Feb  1 17:19:24 raspberrypi upsmon[734]: UPS jaredoffice@localhost on line power
                            

                            Back to the config files we go!
                            /etc/nut/upssched.conf

                            # PIPEFN <filename>
                            # This is commented out by default to make you visit this file and think
                            # about how your system works before potentially opening a hole.
                            

                            FFS, but it gets better! Right below that, also commented out.

                            # LOCKFN <filename>
                            #
                            # REQUIRED.  This was added after version 1.2.1.
                            #
                            # upssched needs to be able to create this filename in order to avoid
                            # a race condition when two events are dispatched from upsmon at nearly
                            # the same time.  This file will only exist briefly.  It must not be
                            # created by any other process.
                            #
                            # You should put this in the same directory as PIPEFN.
                            #
                            

                            So I update the config and make a directory forgetting to chown it from root /sigh...

                            PIPEFN /etc/nut/upssched/upssched.pipe
                            LOCKFN /etc/nut/upssched/upssched.lock
                            1 Reply Last reply Reply Quote 0
                            • JaredBuschJ
                              JaredBusch
                              last edited by JaredBusch

                              Once it was all chowned...

                              Feb  1 17:33:08 raspberrypi upssched[793]: Timer daemon started
                              Feb  1 17:33:09 raspberrypi upssched[793]: New timer: onbattwarn (30 seconds)
                              Feb  1 17:33:39 raspberrypi upssched[793]: Event: onbattwarn
                              Feb  1 17:33:54 raspberrypi upssched[793]: Timer queue empty, exiting
                              

                              And output to the screen:

                              Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:33:39 2017):
                              
                              The UPS is currently running on battery power!
                              
                              1 Reply Last reply Reply Quote 0
                              • JaredBuschJ
                                JaredBusch
                                last edited by

                                Now time to wipe, replicate, test and document.

                                Then the command can be changed to send email.

                                1 Reply Last reply Reply Quote 3
                                • JaredBuschJ
                                  JaredBusch
                                  last edited by JaredBusch

                                  Following my own notes from post 62
                                  At step 11 (installing nut form repo) I see an error.
                                  May or may not have gotten this the first time around..

                                  pi@bna-pwr-pi-01:~ $ sudo apt-get install nut
                                  Reading package lists... Done
                                  <snip>
                                  Unpacking nut (2.7.2-4) ...
                                  Processing triggers for man-db (2.7.0.2-5) ...
                                  Processing triggers for systemd (215-17+deb8u6) ...
                                  Setting up libnspr4:armhf (2:4.12-1+debu8u1) ...
                                  Setting up libnss3:armhf (2:3.26-1+debu8u1) ...
                                  Setting up libupsclient4:armhf (2.7.2-4) ...
                                  Setting up nut-client (2.7.2-4) ...
                                  Job for nut-monitor.service failed. See 'systemctl status nut-monitor.service' and 'journalctl -xn' for details.
                                  invoke-rc.d: initscript nut-client, action "start" failed.
                                  Setting up nut-server (2.7.2-4) ...
                                  A dependency job for nut-server.service failed. See 'journalctl -xn' for details.
                                  invoke-rc.d: initscript nut-server, action "start" failed.
                                  Job for nut-driver.service failed. See 'systemctl status nut-driver.service' and 'journalctl -xn' for details.
                                  Setting up nut (2.7.2-4) ...
                                  Processing triggers for libc-bin (2.19-18+deb8u7) ...
                                  Processing triggers for systemd (215-17+deb8u6) ...
                                  pi@bna-pwr-pi-01:~ $ systemctl status nut-monitor
                                  ● nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller
                                     Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled)
                                     Active: failed (Result: resources) since Thu 2017-02-02 02:10:27 UTC; 49s ago
                                  pi@bna-pwr-pi-01:~ $ 
                                  
                                  1 Reply Last reply Reply Quote 0
                                  • JaredBuschJ
                                    JaredBusch
                                    last edited by

                                    ah here we go, this is normal because not configured.

                                    pi@bna-pwr-pi-01:~ $ sudo journalctl -xn
                                    -- Logs begin at Fri 2016-11-25 18:24:08 UTC, end at Thu 2017-02-02 02:33:03 UTC. --
                                    Feb 02 02:32:47 bna-pwr-pi-01 sudo[23103]: pam_unix(sudo:session): session opened for user root by pi(uid=0)
                                    Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Starting Network UPS Tools - power device monitor and shutdown controller...
                                    -- Subject: Unit nut-monitor.service has begun with start-up
                                    -- Defined-By: systemd
                                    -- Support: http://lists.freedesktop.org/mailman/listinfo/systemd-devel
                                    -- 
                                    -- Unit nut-monitor.service has begun starting up.
                                    Feb 02 02:32:47 bna-pwr-pi-01 upsmon[23113]: upsmon disabled, please adjust the configuration to your needs
                                    Feb 02 02:32:47 bna-pwr-pi-01 upsmon[23113]: Then set MODE to a suitable value in /etc/nut/nut.conf to enable it
                                    Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: PID file /var/run/nut/upsmon.pid not readable (yet?) after start.
                                    Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Failed to start Network UPS Tools - power device monitor and shutdown controller.
                                    -- Subject: Unit nut-monitor.service has failed
                                    -- Defined-By: systemd
                                    -- Support: http://lists.freedesktop.org/mailman/listinfo/systemd-devel
                                    -- 
                                    -- Unit nut-monitor.service has failed.
                                    -- 
                                    -- The result is failed.
                                    Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Unit nut-monitor.service entered failed state.
                                    Feb 02 02:32:48 bna-pwr-pi-01 sudo[23103]: pam_unix(sudo:session): session closed for user root
                                    Feb 02 02:33:03 bna-pwr-pi-01 sudo[23121]: pi : TTY=pts/0 ; PWD=/home/pi ; USER=root ; COMMAND=/bin/journalctl -xn
                                    Feb 02 02:33:03 bna-pwr-pi-01 sudo[23121]: pam_unix(sudo:session): session opened for user root by pi(uid=0)
                                    
                                    1 Reply Last reply Reply Quote 1
                                    • JaredBuschJ
                                      JaredBusch
                                      last edited by JaredBusch

                                      So on to configuration. Nut has only a few config files you need to deal with.

                                      We will go right down the list.

                                      pi@bna-pwr-pi-01:~ $ ls -l /etc/nut
                                      total 44
                                      -rw-r----- 1 root nut  1538 Mar 26  2015 nut.conf
                                      -rw-r----- 1 root nut  4572 Mar 26  2015 ups.conf
                                      -rw-r----- 1 root nut  4578 Mar 26  2015 upsd.conf
                                      -rw-r----- 1 root nut  2131 Mar 26  2015 upsd.users
                                      -rw-r----- 1 root nut 15170 Mar 26  2015 upsmon.conf
                                      -rw-r----- 1 root nut  3887 Mar 26  2015 upssched.conf
                                      
                                      1 Reply Last reply Reply Quote 0
                                      • JaredBuschJ
                                        JaredBusch
                                        last edited by

                                        First up is nut.conf. There is only a single option to set in this file, but it is important.

                                        Assuming you are going to have only one device, or if multiple devices, that they will report in on their own, the simplest configuration is to choose standalone

                                        MODE=standalone
                                        

                                        Here are the various meanings from the conf file.

                                        # - none: NUT is not configured, or use the Integrated Power Management, or use
                                        #   some external system to startup NUT components. So nothing is to be started.
                                        # - standalone: This mode address a local only configuration, with 1 UPS
                                        #   protecting the local system. This implies to start the 3 NUT layers (driver,
                                        #   upsd and upsmon) and the matching configuration files. This mode can also
                                        #   address UPS redundancy.
                                        # - netserver: same as for the standalone configuration, but also need
                                        #   some more network access controls (firewall, tcp-wrappers) and possibly a
                                        #   specific LISTEN directive in upsd.conf.
                                        #   Since this MODE is opened to the network, a special care should be applied
                                        #   to security concerns.
                                        # - netclient: this mode only requires upsmon.
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • JaredBuschJ
                                          JaredBusch
                                          last edited by

                                          Next up is ups.conf, again read the config file for more information, it is fairly thorough.

                                          In this case I am going to connect it to the APC unit pictured at the beginning of this thread.

                                          [bnajaredrouter]
                                          driver = usbhid-ups
                                          port = auto
                                          desc = "Jared Router UPS"
                                          
                                          1 Reply Last reply Reply Quote 0
                                          • JaredBuschJ
                                            JaredBusch
                                            last edited by

                                            The file upsd.conf does not need modified for a typical standalone setup.

                                            1 Reply Last reply Reply Quote 0