    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • gjacobseG
      gjacobse
      last edited by gjacobse

      Well - while I don't have a Pi yet, I do happen to have a LM 17.x system running as my Pandora Music box (Pithos). It's within reach of one of the several UPS units I have (I have like nine) so I used your process and got one set up:

      sudo upsc pandora
      :
      Init SSL without certificate database
      battery.charge: 100
      battery.charge.low: 10
      battery.charge.warning: 50
      battery.date: not set
      battery.mfr.date: 2014/06/22
      battery.runtime: 3336
      battery.runtime.low: 120
      battery.type: PbAc
      battery.voltage: 13.5
      battery.voltage.nominal: 12.0
      device.mfr: APC
      device.model: Back-UPS ES 550G
      device.serial: 4B1425P54201
      device.type: ups
      driver.name: usbhid-ups
      driver.parameter.pollfreq: 30
      driver.parameter.pollinterval: 2
      driver.parameter.port: auto
      driver.version: 2.7.1
      driver.version.data: APC HID 0.95
      driver.version.internal: 0.38
      input.sensitivity: medium
      input.transfer.high: 139
      input.transfer.low: 92
      input.voltage: 125.0
      input.voltage.nominal: 120
      ups.beeper.status: enabled
      ups.delay.shutdown: 20
      ups.firmware: 904.W1 .D
      ups.firmware.aux: W1
      ups.load: 12
      ups.mfr: APC
      ups.mfr.date: 2014/06/22
      ups.model: Back-UPS ES 550G
      ups.productid: 0002
      ups.serial: 4B1425P54201
      ups.status: OL
      ups.timer.reboot: 0
      ups.timer.shutdown: -1
      ups.vendorid: 051d
      
      1 Reply Last reply Reply Quote 1
      • JaredBuschJ
        JaredBusch
        last edited by

        Today will be tinkering with notification options.

        1 Reply Last reply Reply Quote 2
        • gjacobseG
          gjacobse
          last edited by

          Just got this:

          Init SSL without certificate database
          Error: Data stale
          
          1 Reply Last reply Reply Quote 0
          • gjacobseG
            gjacobse
            last edited by

            Went back through the commands above to validation / confirmation:

            $ sudo nano /etc/nut/nut.conf
            

            no changes - the same.

            $ sudo nano /etc/nut/ups.conf
            

            no changes - the same

             $ sudo upsdrvctl start
            Network UPS Tools - UPS driver controller 2.7.1
            Network UPS Tools - Generic HID driver 0.38 (2.7.1)
            USB communication driver 0.32
            Duplicate driver instance detected! Terminating other driver!
            Using subdriver: APC HID 0.95
            

            Okay - seems 'ok'

            $ sudo upsd
            Network UPS Tools upsd 2.7.1
            fopen /var/run/nut/upsd.pid: No such file or directory
            not listening on 127.0.0.1 port 3493
            not listening on ::1 port 3493
            no listening interface available
            
            $ sudo upsc pandora
            Init SSL without certificate database
            Error: Data stale
            

            curious.

            JaredBuschJ 1 Reply Last reply Reply Quote 0
            • JaredBuschJ
              JaredBusch @gjacobse
              last edited by

              @gjacobse I do not get that. Mine has been untouched since last night.

              pi@raspberrypi:~ $ sudo upsc jaredoffice
              Init SSL without certificate database
              battery.charge: 100
              battery.charge.low: 10
              battery.charge.warning: 50
              battery.date: 2001/09/25
              battery.mfr.date: 2010/12/15
              battery.runtime: 1472
              battery.runtime.low: 120
              battery.type: PbAc
              battery.voltage: 27.2
              battery.voltage.nominal: 24.0
              device.mfr: American Power Conversion
              device.model: Back-UPS BR1000G
              device.serial: 3B1051X20329
              device.type: ups
              driver.name: usbhid-ups
              driver.parameter.pollfreq: 30
              driver.parameter.pollinterval: 2
              driver.parameter.port: auto
              driver.version: 2.7.2
              driver.version.data: APC HID 0.95
              driver.version.internal: 0.38
              input.sensitivity: medium
              input.transfer.high: 147
              input.transfer.low: 88
              input.voltage: 124.0
              input.voltage.nominal: 120
              ups.beeper.status: enabled
              ups.delay.shutdown: 20
              ups.firmware: 868.L1 .D
              ups.firmware.aux: L1
              ups.load: 20
              ups.mfr: American Power Conversion
              ups.mfr.date: 2010/12/15
              ups.model: Back-UPS BR1000G
              ups.productid: 0002
              ups.realpower.nominal: 600
              ups.serial: 3B1051X20329
              ups.status: OL
              ups.test.result: No test initiated
              ups.timer.reboot: 0
              ups.timer.shutdown: -1
              ups.vendorid: 051d
              pi@raspberrypi:~ $
              
              1 Reply Last reply Reply Quote 0
              • JaredBuschJ
                JaredBusch
                last edited by

                This is what I will be following to configure reporting/alerting.
                http://www.techrepublic.com/article/customize-ups-related-alerts-in-nut/

                gjacobseG 1 Reply Last reply Reply Quote 1
                • gjacobseG
                  gjacobse @JaredBusch
                  last edited by

                  @JaredBusch
                  Well push comes to Meh -okay. I restarted the box and it's polls now.

                  Won't do anything else with it for a spell to see if it retains it. It's been four days since I restarted it. Now - to reconnect to it as I had to pull the monitor off. X2Go works great,.. but only once I've signed in at the local. sure that is omething that can be changed.

                  1 Reply Last reply Reply Quote 0
                  • gjacobseG
                    gjacobse
                    last edited by

                    checking on my UPS this morning

                     ~ $ uptime
                     09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                    
                     ~ $ sudo upsc pandora
                    Init SSL without certificate database
                    battery.charge: 100
                    battery.charge.low: 10
                    battery.charge.warning: 50
                    battery.date: not set
                    battery.mfr.date: 2014/06/22
                    battery.runtime: 3172
                    battery.runtime.low: 120
                    battery.type: PbAc
                    battery.voltage: 13.6
                    battery.voltage.nominal: 12.0
                    device.mfr: APC
                    device.model: Back-UPS ES 550G
                    device.serial: 4B1425P54201
                    device.type: ups
                    driver.name: usbhid-ups
                    driver.parameter.pollfreq: 30
                    driver.parameter.pollinterval: 2
                    driver.parameter.port: auto
                    driver.version: 2.7.1
                    driver.version.data: APC HID 0.95
                    driver.version.internal: 0.38
                    input.sensitivity: medium
                    input.transfer.high: 139
                    input.transfer.low: 92
                    input.voltage: 126.0
                    input.voltage.nominal: 120
                    ups.beeper.status: enabled
                    ups.delay.shutdown: 20
                    ups.firmware: 904.W1 .D
                    ups.firmware.aux: W1
                    ups.load: 13
                    ups.mfr: APC
                    ups.mfr.date: 2014/06/22
                    ups.model: Back-UPS ES 550G
                    ups.productid: 0002
                    ups.serial: 4B1425P54201
                    ups.status: OL
                    ups.timer.reboot: 0
                    ups.timer.shutdown: -1
                    ups.vendorid: 051d
                    

                    Since reboot, the monitor has been running all the time. So it may have been simply that.

                    As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                    gjacobseG travisdh1T thwrT 3 Replies Last reply Reply Quote 1
                    • gjacobseG
                      gjacobse @gjacobse
                      last edited by

                      @gjacobse said in Pi as a UPS monitor:

                      checking on my UPS this morning

                      Since reboot, the monitor has been running all the time. So it may have been simply that.

                      As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                      Maybe something similar to the UBNT controller software - central configuration ability.....

                      1 Reply Last reply Reply Quote 0
                      • travisdh1T
                        travisdh1 @gjacobse
                        last edited by

                        @gjacobse said in Pi as a UPS monitor:

                        checking on my UPS this morning

                         ~ $ uptime
                         09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                        
                         ~ $ sudo upsc pandora
                        Init SSL without certificate database
                        battery.charge: 100
                        battery.charge.low: 10
                        battery.charge.warning: 50
                        battery.date: not set
                        battery.mfr.date: 2014/06/22
                        battery.runtime: 3172
                        battery.runtime.low: 120
                        battery.type: PbAc
                        battery.voltage: 13.6
                        battery.voltage.nominal: 12.0
                        device.mfr: APC
                        device.model: Back-UPS ES 550G
                        device.serial: 4B1425P54201
                        device.type: ups
                        driver.name: usbhid-ups
                        driver.parameter.pollfreq: 30
                        driver.parameter.pollinterval: 2
                        driver.parameter.port: auto
                        driver.version: 2.7.1
                        driver.version.data: APC HID 0.95
                        driver.version.internal: 0.38
                        input.sensitivity: medium
                        input.transfer.high: 139
                        input.transfer.low: 92
                        input.voltage: 126.0
                        input.voltage.nominal: 120
                        ups.beeper.status: enabled
                        ups.delay.shutdown: 20
                        ups.firmware: 904.W1 .D
                        ups.firmware.aux: W1
                        ups.load: 13
                        ups.mfr: APC
                        ups.mfr.date: 2014/06/22
                        ups.model: Back-UPS ES 550G
                        ups.productid: 0002
                        ups.serial: 4B1425P54201
                        ups.status: OL
                        ups.timer.reboot: 0
                        ups.timer.shutdown: -1
                        ups.vendorid: 051d
                        

                        Since reboot, the monitor has been running all the time. So it may have been simply that.

                        As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                        Take the output of upsc and throw it up on a web page. Unless you want a local display, in which case it's actually more difficult.

                        1 Reply Last reply Reply Quote 0
                        • thwrT
                          thwr @gjacobse
                          last edited by

                          @gjacobse said in Pi as a UPS monitor:

                          checking on my UPS this morning

                           ~ $ uptime
                           09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                          
                           ~ $ sudo upsc pandora
                          Init SSL without certificate database
                          battery.charge: 100
                          battery.charge.low: 10
                          battery.charge.warning: 50
                          battery.date: not set
                          battery.mfr.date: 2014/06/22
                          battery.runtime: 3172
                          battery.runtime.low: 120
                          battery.type: PbAc
                          battery.voltage: 13.6
                          battery.voltage.nominal: 12.0
                          device.mfr: APC
                          device.model: Back-UPS ES 550G
                          device.serial: 4B1425P54201
                          device.type: ups
                          driver.name: usbhid-ups
                          driver.parameter.pollfreq: 30
                          driver.parameter.pollinterval: 2
                          driver.parameter.port: auto
                          driver.version: 2.7.1
                          driver.version.data: APC HID 0.95
                          driver.version.internal: 0.38
                          input.sensitivity: medium
                          input.transfer.high: 139
                          input.transfer.low: 92
                          input.voltage: 126.0
                          input.voltage.nominal: 120
                          ups.beeper.status: enabled
                          ups.delay.shutdown: 20
                          ups.firmware: 904.W1 .D
                          ups.firmware.aux: W1
                          ups.load: 13
                          ups.mfr: APC
                          ups.mfr.date: 2014/06/22
                          ups.model: Back-UPS ES 550G
                          ups.productid: 0002
                          ups.serial: 4B1425P54201
                          ups.status: OL
                          ups.timer.reboot: 0
                          ups.timer.shutdown: -1
                          ups.vendorid: 051d
                          

                          Since reboot, the monitor has been running all the time. So it may have been simply that.

                          As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                          AMQP / MQTT may be awesome for this at the transport layer. MQTT is an interesting protocol that let you define a "last will and testament" action in case something goes south.

                          Ansible/Puppet etc. can handle the central configuration.

                          1 Reply Last reply Reply Quote 1
                          • JaredBuschJ
                            JaredBusch
                            last edited by

                            Hey 3 months later.....

                            1 Reply Last reply Reply Quote 1
                            • JaredBuschJ
                              JaredBusch
                              last edited by

                              Alright, I plugged the thing back in and got to testing.

                              Yeah! It still communicates.

                              pi@raspberrypi:~ $ sudo upsc jaredoffice
                              Init SSL without certificate database
                              battery.charge: 84
                              battery.charge.low: 10
                              battery.charge.warning: 50
                              battery.date: 2001/09/25
                              battery.mfr.date: 2010/12/15
                              battery.runtime: 1236
                              battery.runtime.low: 120
                              battery.type: PbAc
                              battery.voltage: 27.0
                              battery.voltage.nominal: 24.0
                              device.mfr: American Power Conversion
                              device.model: Back-UPS BR1000G
                              device.serial: 3B1051X20329
                              device.type: ups
                              driver.name: usbhid-ups
                              driver.parameter.pollfreq: 30
                              driver.parameter.pollinterval: 2
                              driver.parameter.port: auto
                              driver.version: 2.7.2
                              driver.version.data: APC HID 0.95
                              driver.version.internal: 0.38
                              input.sensitivity: medium
                              input.transfer.high: 147
                              input.transfer.low: 88
                              input.transfer.reason: input voltage out of range
                              input.voltage: 124.0
                              input.voltage.nominal: 120
                              ups.beeper.status: enabled
                              ups.delay.shutdown: 20
                              ups.firmware: 868.L1 .D
                              ups.firmware.aux: L1
                              ups.load: 20
                              ups.mfr: American Power Conversion
                              ups.mfr.date: 2010/12/15
                              ups.model: Back-UPS BR1000G
                              ups.productid: 0002
                              ups.realpower.nominal: 600
                              ups.serial: 3B1051X20329
                              ups.status: OL CHRG
                              ups.test.result: No test initiated
                              ups.timer.reboot: 0
                              ups.timer.shutdown: -1
                              ups.vendorid: 051d
                              
                              1 Reply Last reply Reply Quote 3
                              • JaredBuschJ
                                JaredBusch
                                last edited by JaredBusch

                                Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                                Ok back to the manual and checking the conf files.

                                Well it would probably help if I told the thing what to monitor..
                                /etc/nut/upsmon.conf

                                MONITOR jaredoffice@localhost 1 upsmon demo master
                                

                                Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                                pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                                # put at end of file
                                [upsmon]
                                password = demo
                                upsmon master
                                

                                Now reload the monitor

                                pi@raspberrypi:~ $ sudo upsmon -c reload
                                Network UPS Tools upsmon 2.7.2
                                pi@raspberrypi:~ $
                                

                                Then unplug the UPS. and get nothing.

                                look in the logs..
                                tail/var/log/syslog

                                Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                                Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                                Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                                Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                                Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                                

                                Say to yourself, WTF did I do 3 months ago....

                                Time to reload and start over.

                                gjacobseG 1 Reply Last reply Reply Quote 0
                                • gjacobseG
                                  gjacobse @JaredBusch
                                  last edited by

                                  @JaredBusch said in Pi as a UPS monitor:

                                  Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                                  Ok back to the manual and checking the conf files.

                                  Well it would probably help if I told the thing what to monitor..
                                  /etc/nut/upsmon.conf

                                  MONITOR jaredoffice@localhost 1 upsmon demo master
                                  

                                  Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                                  pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                                  # put at end of file
                                  [upsmon]
                                  password = demo
                                  upsmon master
                                  

                                  Now reload the monitor

                                  pi@raspberrypi:~ $ sudo upsmon -c reload
                                  Network UPS Tools upsmon 2.7.2
                                  pi@raspberrypi:~ $
                                  

                                  Then unplug the UPS. and get nothing.

                                  look in the logs..
                                  tail/var/log/syslog

                                  Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                                  Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                                  Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                                  Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                                  Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                                  

                                  Say to yourself, WTF did I do 3 months ago....

                                  Time to reload and start over.

                                  think i got the same thing, and decide the same course of action, to which I have not moved forward with. Albeit, it's not on a rPi but a desktop - premise is the same.

                                  Think we may have to create a user for the NUT system.... but again,.. can't work with it right now.

                                  1 Reply Last reply Reply Quote 0
                                  • JaredBuschJ
                                    JaredBusch
                                    last edited by JaredBusch

                                    Quick check of upsmon.conf found this, uncommented it.

                                    # RUN_AS_USER nut
                                    

                                    Rebooted Pi, unplugged UPS.

                                    Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:04 2017):
                                    
                                    UPS jaredoffice@localhost on battery
                                    
                                    
                                    Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:24 2017):
                                    
                                    UPS jaredoffice@localhost on line power
                                    
                                    1 Reply Last reply Reply Quote 0
                                    • JaredBuschJ
                                      JaredBusch
                                      last edited by

                                      Syslog had this though.

                                      Feb  1 17:19:04 raspberrypi upsmon[734]: UPS jaredoffice@localhost on battery
                                      Feb  1 17:19:11 raspberrypi upssched[792]: Failed to connect to parent and failed to create parent: No such file or directory
                                      Feb  1 17:19:24 raspberrypi upsmon[734]: UPS jaredoffice@localhost on line power
                                      

                                      Back to the config files we go!
                                      /etc/nut/upssched.conf

                                      # PIPEFN <filename>
                                      # This is commented out by default to make you visit this file and think
                                      # about how your system works before potentially opening a hole.
                                      

                                      FFS, but it gets better! Right below that, also commented out.

                                      # LOCKFN <filename>
                                      #
                                      # REQUIRED.  This was added after version 1.2.1.
                                      #
                                      # upssched needs to be able to create this filename in order to avoid
                                      # a race condition when two events are dispatched from upsmon at nearly
                                      # the same time.  This file will only exist briefly.  It must not be
                                      # created by any other process.
                                      #
                                      # You should put this in the same directory as PIPEFN.
                                      #
                                      

                                      So I update the config and make a directory forgetting to chown it from root /sigh...

                                      PIPEFN /etc/nut/upssched/upssched.pipe
                                      LOCKFN /etc/nut/upssched/upssched.lock
                                      1 Reply Last reply Reply Quote 0
                                      • JaredBuschJ
                                        JaredBusch
                                        last edited by JaredBusch

                                        Once it was all chowned...

                                        Feb  1 17:33:08 raspberrypi upssched[793]: Timer daemon started
                                        Feb  1 17:33:09 raspberrypi upssched[793]: New timer: onbattwarn (30 seconds)
                                        Feb  1 17:33:39 raspberrypi upssched[793]: Event: onbattwarn
                                        Feb  1 17:33:54 raspberrypi upssched[793]: Timer queue empty, exiting
                                        

                                        And output to the screen:

                                        Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:33:39 2017):
                                        
                                        The UPS is currently running on battery power!
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • JaredBuschJ
                                          JaredBusch
                                          last edited by

                                          Now time to wipe, replicate, test and document.

                                          Then the command can be changed to send email.

                                          1 Reply Last reply Reply Quote 3
                                          • JaredBuschJ
                                            JaredBusch
                                            last edited by JaredBusch

                                            Following my own notes from post 62
                                            At step 11 (installing nut form repo) I see an error.
                                            May or may not have gotten this the first time around..

                                            pi@bna-pwr-pi-01:~ $ sudo apt-get install nut
                                            Reading package lists... Done
                                            <snip>
                                            Unpacking nut (2.7.2-4) ...
                                            Processing triggers for man-db (2.7.0.2-5) ...
                                            Processing triggers for systemd (215-17+deb8u6) ...
                                            Setting up libnspr4:armhf (2:4.12-1+debu8u1) ...
                                            Setting up libnss3:armhf (2:3.26-1+debu8u1) ...
                                            Setting up libupsclient4:armhf (2.7.2-4) ...
                                            Setting up nut-client (2.7.2-4) ...
                                            Job for nut-monitor.service failed. See 'systemctl status nut-monitor.service' and 'journalctl -xn' for details.
                                            invoke-rc.d: initscript nut-client, action "start" failed.
                                            Setting up nut-server (2.7.2-4) ...
                                            A dependency job for nut-server.service failed. See 'journalctl -xn' for details.
                                            invoke-rc.d: initscript nut-server, action "start" failed.
                                            Job for nut-driver.service failed. See 'systemctl status nut-driver.service' and 'journalctl -xn' for details.
                                            Setting up nut (2.7.2-4) ...
                                            Processing triggers for libc-bin (2.19-18+deb8u7) ...
                                            Processing triggers for systemd (215-17+deb8u6) ...
                                            pi@bna-pwr-pi-01:~ $ systemctl status nut-monitor
                                            ● nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller
                                               Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled)
                                               Active: failed (Result: resources) since Thu 2017-02-02 02:10:27 UTC; 49s ago
                                            pi@bna-pwr-pi-01:~ $ 
                                            