    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • gjacobseG
      gjacobse
      last edited by

      Interesting that the last two of the last three messages seem out of order. But - great information.

      1 Reply Last reply Reply Quote 0
      • gjacobseG
        gjacobse
        last edited by gjacobse

        Well - while I don't have a Pi yet, I do happen to have a LM 17.x system running as my Pandora Music box (Pithos). It's within reach of one of the several UPS units I have (I have like nine) so I used your process and got one set up:

        sudo upsc pandora
        :
        Init SSL without certificate database
        battery.charge: 100
        battery.charge.low: 10
        battery.charge.warning: 50
        battery.date: not set
        battery.mfr.date: 2014/06/22
        battery.runtime: 3336
        battery.runtime.low: 120
        battery.type: PbAc
        battery.voltage: 13.5
        battery.voltage.nominal: 12.0
        device.mfr: APC
        device.model: Back-UPS ES 550G
        device.serial: 4B1425P54201
        device.type: ups
        driver.name: usbhid-ups
        driver.parameter.pollfreq: 30
        driver.parameter.pollinterval: 2
        driver.parameter.port: auto
        driver.version: 2.7.1
        driver.version.data: APC HID 0.95
        driver.version.internal: 0.38
        input.sensitivity: medium
        input.transfer.high: 139
        input.transfer.low: 92
        input.voltage: 125.0
        input.voltage.nominal: 120
        ups.beeper.status: enabled
        ups.delay.shutdown: 20
        ups.firmware: 904.W1 .D
        ups.firmware.aux: W1
        ups.load: 12
        ups.mfr: APC
        ups.mfr.date: 2014/06/22
        ups.model: Back-UPS ES 550G
        ups.productid: 0002
        ups.serial: 4B1425P54201
        ups.status: OL
        ups.timer.reboot: 0
        ups.timer.shutdown: -1
        ups.vendorid: 051d
        
        1 Reply Last reply Reply Quote 1
        • JaredBuschJ
          JaredBusch
          last edited by

          Today will be tinkering with notification options.

          1 Reply Last reply Reply Quote 2
          • gjacobseG
            gjacobse
            last edited by

            Just got this:

            Init SSL without certificate database
            Error: Data stale
            
            1 Reply Last reply Reply Quote 0
            • gjacobseG
              gjacobse
              last edited by

              Went back through the commands above to validation / confirmation:

              $ sudo nano /etc/nut/nut.conf
              

              no changes - the same.

              $ sudo nano /etc/nut/ups.conf
              

              no changes - the same

               $ sudo upsdrvctl start
              Network UPS Tools - UPS driver controller 2.7.1
              Network UPS Tools - Generic HID driver 0.38 (2.7.1)
              USB communication driver 0.32
              Duplicate driver instance detected! Terminating other driver!
              Using subdriver: APC HID 0.95
              

              Okay - seems 'ok'

              $ sudo upsd
              Network UPS Tools upsd 2.7.1
              fopen /var/run/nut/upsd.pid: No such file or directory
              not listening on 127.0.0.1 port 3493
              not listening on ::1 port 3493
              no listening interface available
              
              $ sudo upsc pandora
              Init SSL without certificate database
              Error: Data stale
              

              curious.

              JaredBuschJ 1 Reply Last reply Reply Quote 0
              • JaredBuschJ
                JaredBusch @gjacobse
                last edited by

                @gjacobse I do not get that. Mine has been untouched since last night.

                pi@raspberrypi:~ $ sudo upsc jaredoffice
                Init SSL without certificate database
                battery.charge: 100
                battery.charge.low: 10
                battery.charge.warning: 50
                battery.date: 2001/09/25
                battery.mfr.date: 2010/12/15
                battery.runtime: 1472
                battery.runtime.low: 120
                battery.type: PbAc
                battery.voltage: 27.2
                battery.voltage.nominal: 24.0
                device.mfr: American Power Conversion
                device.model: Back-UPS BR1000G
                device.serial: 3B1051X20329
                device.type: ups
                driver.name: usbhid-ups
                driver.parameter.pollfreq: 30
                driver.parameter.pollinterval: 2
                driver.parameter.port: auto
                driver.version: 2.7.2
                driver.version.data: APC HID 0.95
                driver.version.internal: 0.38
                input.sensitivity: medium
                input.transfer.high: 147
                input.transfer.low: 88
                input.voltage: 124.0
                input.voltage.nominal: 120
                ups.beeper.status: enabled
                ups.delay.shutdown: 20
                ups.firmware: 868.L1 .D
                ups.firmware.aux: L1
                ups.load: 20
                ups.mfr: American Power Conversion
                ups.mfr.date: 2010/12/15
                ups.model: Back-UPS BR1000G
                ups.productid: 0002
                ups.realpower.nominal: 600
                ups.serial: 3B1051X20329
                ups.status: OL
                ups.test.result: No test initiated
                ups.timer.reboot: 0
                ups.timer.shutdown: -1
                ups.vendorid: 051d
                pi@raspberrypi:~ $
                
                1 Reply Last reply Reply Quote 0
                • JaredBuschJ
                  JaredBusch
                  last edited by

                  This is what I will be following to configure reporting/alerting.
                  http://www.techrepublic.com/article/customize-ups-related-alerts-in-nut/

                  gjacobseG 1 Reply Last reply Reply Quote 1
                  • gjacobseG
                    gjacobse @JaredBusch
                    last edited by

                    @JaredBusch
                    Well push comes to Meh -okay. I restarted the box and it's polls now.

                    Won't do anything else with it for a spell to see if it retains it. It's been four days since I restarted it. Now - to reconnect to it as I had to pull the monitor off. X2Go works great,.. but only once I've signed in at the local. sure that is omething that can be changed.

                    1 Reply Last reply Reply Quote 0
                    • gjacobseG
                      gjacobse
                      last edited by

                      checking on my UPS this morning

                       ~ $ uptime
                       09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                      
                       ~ $ sudo upsc pandora
                      Init SSL without certificate database
                      battery.charge: 100
                      battery.charge.low: 10
                      battery.charge.warning: 50
                      battery.date: not set
                      battery.mfr.date: 2014/06/22
                      battery.runtime: 3172
                      battery.runtime.low: 120
                      battery.type: PbAc
                      battery.voltage: 13.6
                      battery.voltage.nominal: 12.0
                      device.mfr: APC
                      device.model: Back-UPS ES 550G
                      device.serial: 4B1425P54201
                      device.type: ups
                      driver.name: usbhid-ups
                      driver.parameter.pollfreq: 30
                      driver.parameter.pollinterval: 2
                      driver.parameter.port: auto
                      driver.version: 2.7.1
                      driver.version.data: APC HID 0.95
                      driver.version.internal: 0.38
                      input.sensitivity: medium
                      input.transfer.high: 139
                      input.transfer.low: 92
                      input.voltage: 126.0
                      input.voltage.nominal: 120
                      ups.beeper.status: enabled
                      ups.delay.shutdown: 20
                      ups.firmware: 904.W1 .D
                      ups.firmware.aux: W1
                      ups.load: 13
                      ups.mfr: APC
                      ups.mfr.date: 2014/06/22
                      ups.model: Back-UPS ES 550G
                      ups.productid: 0002
                      ups.serial: 4B1425P54201
                      ups.status: OL
                      ups.timer.reboot: 0
                      ups.timer.shutdown: -1
                      ups.vendorid: 051d
                      

                      Since reboot, the monitor has been running all the time. So it may have been simply that.

                      As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                      gjacobseG travisdh1T thwrT 3 Replies Last reply Reply Quote 1
                      • gjacobseG
                        gjacobse @gjacobse
                        last edited by

                        @gjacobse said in Pi as a UPS monitor:

                        checking on my UPS this morning

                        Since reboot, the monitor has been running all the time. So it may have been simply that.

                        As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                        Maybe something similar to the UBNT controller software - central configuration ability.....

                        1 Reply Last reply Reply Quote 0
                        • travisdh1T
                          travisdh1 @gjacobse
                          last edited by

                          @gjacobse said in Pi as a UPS monitor:

                          checking on my UPS this morning

                           ~ $ uptime
                           09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                          
                           ~ $ sudo upsc pandora
                          Init SSL without certificate database
                          battery.charge: 100
                          battery.charge.low: 10
                          battery.charge.warning: 50
                          battery.date: not set
                          battery.mfr.date: 2014/06/22
                          battery.runtime: 3172
                          battery.runtime.low: 120
                          battery.type: PbAc
                          battery.voltage: 13.6
                          battery.voltage.nominal: 12.0
                          device.mfr: APC
                          device.model: Back-UPS ES 550G
                          device.serial: 4B1425P54201
                          device.type: ups
                          driver.name: usbhid-ups
                          driver.parameter.pollfreq: 30
                          driver.parameter.pollinterval: 2
                          driver.parameter.port: auto
                          driver.version: 2.7.1
                          driver.version.data: APC HID 0.95
                          driver.version.internal: 0.38
                          input.sensitivity: medium
                          input.transfer.high: 139
                          input.transfer.low: 92
                          input.voltage: 126.0
                          input.voltage.nominal: 120
                          ups.beeper.status: enabled
                          ups.delay.shutdown: 20
                          ups.firmware: 904.W1 .D
                          ups.firmware.aux: W1
                          ups.load: 13
                          ups.mfr: APC
                          ups.mfr.date: 2014/06/22
                          ups.model: Back-UPS ES 550G
                          ups.productid: 0002
                          ups.serial: 4B1425P54201
                          ups.status: OL
                          ups.timer.reboot: 0
                          ups.timer.shutdown: -1
                          ups.vendorid: 051d
                          

                          Since reboot, the monitor has been running all the time. So it may have been simply that.

                          As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                          Take the output of upsc and throw it up on a web page. Unless you want a local display, in which case it's actually more difficult.

                          1 Reply Last reply Reply Quote 0
                          • thwrT
                            thwr @gjacobse
                            last edited by

                            @gjacobse said in Pi as a UPS monitor:

                            checking on my UPS this morning

                             ~ $ uptime
                             09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                            
                             ~ $ sudo upsc pandora
                            Init SSL without certificate database
                            battery.charge: 100
                            battery.charge.low: 10
                            battery.charge.warning: 50
                            battery.date: not set
                            battery.mfr.date: 2014/06/22
                            battery.runtime: 3172
                            battery.runtime.low: 120
                            battery.type: PbAc
                            battery.voltage: 13.6
                            battery.voltage.nominal: 12.0
                            device.mfr: APC
                            device.model: Back-UPS ES 550G
                            device.serial: 4B1425P54201
                            device.type: ups
                            driver.name: usbhid-ups
                            driver.parameter.pollfreq: 30
                            driver.parameter.pollinterval: 2
                            driver.parameter.port: auto
                            driver.version: 2.7.1
                            driver.version.data: APC HID 0.95
                            driver.version.internal: 0.38
                            input.sensitivity: medium
                            input.transfer.high: 139
                            input.transfer.low: 92
                            input.voltage: 126.0
                            input.voltage.nominal: 120
                            ups.beeper.status: enabled
                            ups.delay.shutdown: 20
                            ups.firmware: 904.W1 .D
                            ups.firmware.aux: W1
                            ups.load: 13
                            ups.mfr: APC
                            ups.mfr.date: 2014/06/22
                            ups.model: Back-UPS ES 550G
                            ups.productid: 0002
                            ups.serial: 4B1425P54201
                            ups.status: OL
                            ups.timer.reboot: 0
                            ups.timer.shutdown: -1
                            ups.vendorid: 051d
                            

                            Since reboot, the monitor has been running all the time. So it may have been simply that.

                            As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                            AMQP / MQTT may be awesome for this at the transport layer. MQTT is an interesting protocol that let you define a "last will and testament" action in case something goes south.

                            Ansible/Puppet etc. can handle the central configuration.

                            1 Reply Last reply Reply Quote 1
                            • JaredBuschJ
                              JaredBusch
                              last edited by

                              Hey 3 months later.....

                              1 Reply Last reply Reply Quote 1
                              • JaredBuschJ
                                JaredBusch
                                last edited by

                                Alright, I plugged the thing back in and got to testing.

                                Yeah! It still communicates.

                                pi@raspberrypi:~ $ sudo upsc jaredoffice
                                Init SSL without certificate database
                                battery.charge: 84
                                battery.charge.low: 10
                                battery.charge.warning: 50
                                battery.date: 2001/09/25
                                battery.mfr.date: 2010/12/15
                                battery.runtime: 1236
                                battery.runtime.low: 120
                                battery.type: PbAc
                                battery.voltage: 27.0
                                battery.voltage.nominal: 24.0
                                device.mfr: American Power Conversion
                                device.model: Back-UPS BR1000G
                                device.serial: 3B1051X20329
                                device.type: ups
                                driver.name: usbhid-ups
                                driver.parameter.pollfreq: 30
                                driver.parameter.pollinterval: 2
                                driver.parameter.port: auto
                                driver.version: 2.7.2
                                driver.version.data: APC HID 0.95
                                driver.version.internal: 0.38
                                input.sensitivity: medium
                                input.transfer.high: 147
                                input.transfer.low: 88
                                input.transfer.reason: input voltage out of range
                                input.voltage: 124.0
                                input.voltage.nominal: 120
                                ups.beeper.status: enabled
                                ups.delay.shutdown: 20
                                ups.firmware: 868.L1 .D
                                ups.firmware.aux: L1
                                ups.load: 20
                                ups.mfr: American Power Conversion
                                ups.mfr.date: 2010/12/15
                                ups.model: Back-UPS BR1000G
                                ups.productid: 0002
                                ups.realpower.nominal: 600
                                ups.serial: 3B1051X20329
                                ups.status: OL CHRG
                                ups.test.result: No test initiated
                                ups.timer.reboot: 0
                                ups.timer.shutdown: -1
                                ups.vendorid: 051d
                                
                                1 Reply Last reply Reply Quote 3
                                • JaredBuschJ
                                  JaredBusch
                                  last edited by JaredBusch

                                  Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                                  Ok back to the manual and checking the conf files.

                                  Well it would probably help if I told the thing what to monitor..
                                  /etc/nut/upsmon.conf

                                  MONITOR jaredoffice@localhost 1 upsmon demo master
                                  

                                  Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                                  pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                                  # put at end of file
                                  [upsmon]
                                  password = demo
                                  upsmon master
                                  

                                  Now reload the monitor

                                  pi@raspberrypi:~ $ sudo upsmon -c reload
                                  Network UPS Tools upsmon 2.7.2
                                  pi@raspberrypi:~ $
                                  

                                  Then unplug the UPS. and get nothing.

                                  look in the logs..
                                  tail/var/log/syslog

                                  Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                                  Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                                  Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                                  Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                                  Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                                  

                                  Say to yourself, WTF did I do 3 months ago....

                                  Time to reload and start over.

                                  gjacobseG 1 Reply Last reply Reply Quote 0
                                  • gjacobseG
                                    gjacobse @JaredBusch
                                    last edited by

                                    @JaredBusch said in Pi as a UPS monitor:

                                    Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                                    Ok back to the manual and checking the conf files.

                                    Well it would probably help if I told the thing what to monitor..
                                    /etc/nut/upsmon.conf

                                    MONITOR jaredoffice@localhost 1 upsmon demo master
                                    

                                    Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                                    pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                                    # put at end of file
                                    [upsmon]
                                    password = demo
                                    upsmon master
                                    

                                    Now reload the monitor

                                    pi@raspberrypi:~ $ sudo upsmon -c reload
                                    Network UPS Tools upsmon 2.7.2
                                    pi@raspberrypi:~ $
                                    

                                    Then unplug the UPS. and get nothing.

                                    look in the logs..
                                    tail/var/log/syslog

                                    Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                                    Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                                    Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                                    Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                                    Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                                    

                                    Say to yourself, WTF did I do 3 months ago....

                                    Time to reload and start over.

                                    think i got the same thing, and decide the same course of action, to which I have not moved forward with. Albeit, it's not on a rPi but a desktop - premise is the same.

                                    Think we may have to create a user for the NUT system.... but again,.. can't work with it right now.

                                    1 Reply Last reply Reply Quote 0
                                    • JaredBuschJ
                                      JaredBusch
                                      last edited by JaredBusch

                                      Quick check of upsmon.conf found this, uncommented it.

                                      # RUN_AS_USER nut
                                      

                                      Rebooted Pi, unplugged UPS.

                                      Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:04 2017):
                                      
                                      UPS jaredoffice@localhost on battery
                                      
                                      
                                      Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:24 2017):
                                      
                                      UPS jaredoffice@localhost on line power
                                      
                                      1 Reply Last reply Reply Quote 0
                                      • JaredBuschJ
                                        JaredBusch
                                        last edited by

                                        Syslog had this though.

                                        Feb  1 17:19:04 raspberrypi upsmon[734]: UPS jaredoffice@localhost on battery
                                        Feb  1 17:19:11 raspberrypi upssched[792]: Failed to connect to parent and failed to create parent: No such file or directory
                                        Feb  1 17:19:24 raspberrypi upsmon[734]: UPS jaredoffice@localhost on line power
                                        

                                        Back to the config files we go!
                                        /etc/nut/upssched.conf

                                        # PIPEFN <filename>
                                        # This is commented out by default to make you visit this file and think
                                        # about how your system works before potentially opening a hole.
                                        

                                        FFS, but it gets better! Right below that, also commented out.

                                        # LOCKFN <filename>
                                        #
                                        # REQUIRED.  This was added after version 1.2.1.
                                        #
                                        # upssched needs to be able to create this filename in order to avoid
                                        # a race condition when two events are dispatched from upsmon at nearly
                                        # the same time.  This file will only exist briefly.  It must not be
                                        # created by any other process.
                                        #
                                        # You should put this in the same directory as PIPEFN.
                                        #
                                        

                                        So I update the config and make a directory forgetting to chown it from root /sigh...

                                        PIPEFN /etc/nut/upssched/upssched.pipe
                                        LOCKFN /etc/nut/upssched/upssched.lock
                                        1 Reply Last reply Reply Quote 0
                                        • JaredBuschJ
                                          JaredBusch
                                          last edited by JaredBusch

                                          Once it was all chowned...

                                          Feb  1 17:33:08 raspberrypi upssched[793]: Timer daemon started
                                          Feb  1 17:33:09 raspberrypi upssched[793]: New timer: onbattwarn (30 seconds)
                                          Feb  1 17:33:39 raspberrypi upssched[793]: Event: onbattwarn
                                          Feb  1 17:33:54 raspberrypi upssched[793]: Timer queue empty, exiting
                                          

                                          And output to the screen:

                                          Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:33:39 2017):
                                          
                                          The UPS is currently running on battery power!
                                          
                                          1 Reply Last reply Reply Quote 0
                                          • JaredBuschJ
                                            JaredBusch
                                            last edited by

                                            Now time to wipe, replicate, test and document.

                                            Then the command can be changed to send email.

                                            1 Reply Last reply Reply Quote 3