    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • JaredBuschJ
      JaredBusch
      last edited by

      Hopefully I can get it to do something tomorrow. no more time tonight.

      1 Reply Last reply Reply Quote 0
      • JaredBuschJ
        JaredBusch
        last edited by JaredBusch

        Instructions assuming a Pi3

        1. Install NOOBS to the SD Card.
        2. Boot the Pi to NOOBS
        3. Connect to wifi
        4. Once it sees internet you can choose to install a minimal version of raspbian with no GUI
        5. wait
        6. login with default creds pi/raspberry
        7. run sudo raspi-config to enable SSH and optionally set other options you want.
        8. edit the wifi config file sudo nano /etc/wpa_supplicant/wpa_supplicant.conf
          network={
          ssid="yourssid"
          psk="ssidpassword"
          }
        9. reboot the Pi3
        10. update raspian
          1. sudo apt-get update
          2. sudo apt-get upgrade
        11. Install nut
          1. sudo apt-get install nut
        12. Edit sudo nano /etc/nut/nut.conf
          1. change MODE=standalone
        13. Edit sudo nano /etc/nut/ups.conf
        14. add a block at the end of the file.
          1. a default example
            [somenameforups]
            driver = usbhid-ups
            port = auto
            desc = "Some descriptive name for UPS"
          2. what mine is
            [jaredoffice]
            driver = usbhid-ups
            port = auto
            desc = "Jared's Desk"
        15. Test the conf file is right sudo upsdrvctl start
        16. Launch the UPS daemon sudo upsd
        17. see if it is talking sudo upsc somenameforups@localhost
          1. or my real one sudo upsc jaredoffice@localhost
        1 Reply Last reply Reply Quote 3
        • gjacobseG
          gjacobse
          last edited by

          Interesting that the last two of the last three messages seem out of order. But - great information.

          1 Reply Last reply Reply Quote 0
          • gjacobseG
            gjacobse
            last edited by gjacobse

            Well - while I don't have a Pi yet, I do happen to have a LM 17.x system running as my Pandora Music box (Pithos). It's within reach of one of the several UPS units I have (I have like nine) so I used your process and got one set up:

            sudo upsc pandora
            :
            Init SSL without certificate database
            battery.charge: 100
            battery.charge.low: 10
            battery.charge.warning: 50
            battery.date: not set
            battery.mfr.date: 2014/06/22
            battery.runtime: 3336
            battery.runtime.low: 120
            battery.type: PbAc
            battery.voltage: 13.5
            battery.voltage.nominal: 12.0
            device.mfr: APC
            device.model: Back-UPS ES 550G
            device.serial: 4B1425P54201
            device.type: ups
            driver.name: usbhid-ups
            driver.parameter.pollfreq: 30
            driver.parameter.pollinterval: 2
            driver.parameter.port: auto
            driver.version: 2.7.1
            driver.version.data: APC HID 0.95
            driver.version.internal: 0.38
            input.sensitivity: medium
            input.transfer.high: 139
            input.transfer.low: 92
            input.voltage: 125.0
            input.voltage.nominal: 120
            ups.beeper.status: enabled
            ups.delay.shutdown: 20
            ups.firmware: 904.W1 .D
            ups.firmware.aux: W1
            ups.load: 12
            ups.mfr: APC
            ups.mfr.date: 2014/06/22
            ups.model: Back-UPS ES 550G
            ups.productid: 0002
            ups.serial: 4B1425P54201
            ups.status: OL
            ups.timer.reboot: 0
            ups.timer.shutdown: -1
            ups.vendorid: 051d
            
            1 Reply Last reply Reply Quote 1
            • JaredBuschJ
              JaredBusch
              last edited by

              Today will be tinkering with notification options.

              1 Reply Last reply Reply Quote 2
              • gjacobseG
                gjacobse
                last edited by

                Just got this:

                Init SSL without certificate database
                Error: Data stale
                
                1 Reply Last reply Reply Quote 0
                • gjacobseG
                  gjacobse
                  last edited by

                  Went back through the commands above to validation / confirmation:

                  $ sudo nano /etc/nut/nut.conf
                  

                  no changes - the same.

                  $ sudo nano /etc/nut/ups.conf
                  

                  no changes - the same

                   $ sudo upsdrvctl start
                  Network UPS Tools - UPS driver controller 2.7.1
                  Network UPS Tools - Generic HID driver 0.38 (2.7.1)
                  USB communication driver 0.32
                  Duplicate driver instance detected! Terminating other driver!
                  Using subdriver: APC HID 0.95
                  

                  Okay - seems 'ok'

                  $ sudo upsd
                  Network UPS Tools upsd 2.7.1
                  fopen /var/run/nut/upsd.pid: No such file or directory
                  not listening on 127.0.0.1 port 3493
                  not listening on ::1 port 3493
                  no listening interface available
                  
                  $ sudo upsc pandora
                  Init SSL without certificate database
                  Error: Data stale
                  

                  curious.

                  JaredBuschJ 1 Reply Last reply Reply Quote 0
                  • JaredBuschJ
                    JaredBusch @gjacobse
                    last edited by

                    @gjacobse I do not get that. Mine has been untouched since last night.

                    pi@raspberrypi:~ $ sudo upsc jaredoffice
                    Init SSL without certificate database
                    battery.charge: 100
                    battery.charge.low: 10
                    battery.charge.warning: 50
                    battery.date: 2001/09/25
                    battery.mfr.date: 2010/12/15
                    battery.runtime: 1472
                    battery.runtime.low: 120
                    battery.type: PbAc
                    battery.voltage: 27.2
                    battery.voltage.nominal: 24.0
                    device.mfr: American Power Conversion
                    device.model: Back-UPS BR1000G
                    device.serial: 3B1051X20329
                    device.type: ups
                    driver.name: usbhid-ups
                    driver.parameter.pollfreq: 30
                    driver.parameter.pollinterval: 2
                    driver.parameter.port: auto
                    driver.version: 2.7.2
                    driver.version.data: APC HID 0.95
                    driver.version.internal: 0.38
                    input.sensitivity: medium
                    input.transfer.high: 147
                    input.transfer.low: 88
                    input.voltage: 124.0
                    input.voltage.nominal: 120
                    ups.beeper.status: enabled
                    ups.delay.shutdown: 20
                    ups.firmware: 868.L1 .D
                    ups.firmware.aux: L1
                    ups.load: 20
                    ups.mfr: American Power Conversion
                    ups.mfr.date: 2010/12/15
                    ups.model: Back-UPS BR1000G
                    ups.productid: 0002
                    ups.realpower.nominal: 600
                    ups.serial: 3B1051X20329
                    ups.status: OL
                    ups.test.result: No test initiated
                    ups.timer.reboot: 0
                    ups.timer.shutdown: -1
                    ups.vendorid: 051d
                    pi@raspberrypi:~ $
                    
                    1 Reply Last reply Reply Quote 0
                    • JaredBuschJ
                      JaredBusch
                      last edited by

                      This is what I will be following to configure reporting/alerting.
                      http://www.techrepublic.com/article/customize-ups-related-alerts-in-nut/

                      gjacobseG 1 Reply Last reply Reply Quote 1
                      • gjacobseG
                        gjacobse @JaredBusch
                        last edited by

                        @JaredBusch
                        Well push comes to Meh -okay. I restarted the box and it's polls now.

                        Won't do anything else with it for a spell to see if it retains it. It's been four days since I restarted it. Now - to reconnect to it as I had to pull the monitor off. X2Go works great,.. but only once I've signed in at the local. sure that is omething that can be changed.

                        1 Reply Last reply Reply Quote 0
                        • gjacobseG
                          gjacobse
                          last edited by

                          checking on my UPS this morning

                           ~ $ uptime
                           09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                          
                           ~ $ sudo upsc pandora
                          Init SSL without certificate database
                          battery.charge: 100
                          battery.charge.low: 10
                          battery.charge.warning: 50
                          battery.date: not set
                          battery.mfr.date: 2014/06/22
                          battery.runtime: 3172
                          battery.runtime.low: 120
                          battery.type: PbAc
                          battery.voltage: 13.6
                          battery.voltage.nominal: 12.0
                          device.mfr: APC
                          device.model: Back-UPS ES 550G
                          device.serial: 4B1425P54201
                          device.type: ups
                          driver.name: usbhid-ups
                          driver.parameter.pollfreq: 30
                          driver.parameter.pollinterval: 2
                          driver.parameter.port: auto
                          driver.version: 2.7.1
                          driver.version.data: APC HID 0.95
                          driver.version.internal: 0.38
                          input.sensitivity: medium
                          input.transfer.high: 139
                          input.transfer.low: 92
                          input.voltage: 126.0
                          input.voltage.nominal: 120
                          ups.beeper.status: enabled
                          ups.delay.shutdown: 20
                          ups.firmware: 904.W1 .D
                          ups.firmware.aux: W1
                          ups.load: 13
                          ups.mfr: APC
                          ups.mfr.date: 2014/06/22
                          ups.model: Back-UPS ES 550G
                          ups.productid: 0002
                          ups.serial: 4B1425P54201
                          ups.status: OL
                          ups.timer.reboot: 0
                          ups.timer.shutdown: -1
                          ups.vendorid: 051d
                          

                          Since reboot, the monitor has been running all the time. So it may have been simply that.

                          As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                          gjacobseG travisdh1T thwrT 3 Replies Last reply Reply Quote 1
                          • gjacobseG
                            gjacobse @gjacobse
                            last edited by

                            @gjacobse said in Pi as a UPS monitor:

                            checking on my UPS this morning

                            Since reboot, the monitor has been running all the time. So it may have been simply that.

                            As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                            Maybe something similar to the UBNT controller software - central configuration ability.....

                            1 Reply Last reply Reply Quote 0
                            • travisdh1T
                              travisdh1 @gjacobse
                              last edited by

                              @gjacobse said in Pi as a UPS monitor:

                              checking on my UPS this morning

                               ~ $ uptime
                               09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                              
                               ~ $ sudo upsc pandora
                              Init SSL without certificate database
                              battery.charge: 100
                              battery.charge.low: 10
                              battery.charge.warning: 50
                              battery.date: not set
                              battery.mfr.date: 2014/06/22
                              battery.runtime: 3172
                              battery.runtime.low: 120
                              battery.type: PbAc
                              battery.voltage: 13.6
                              battery.voltage.nominal: 12.0
                              device.mfr: APC
                              device.model: Back-UPS ES 550G
                              device.serial: 4B1425P54201
                              device.type: ups
                              driver.name: usbhid-ups
                              driver.parameter.pollfreq: 30
                              driver.parameter.pollinterval: 2
                              driver.parameter.port: auto
                              driver.version: 2.7.1
                              driver.version.data: APC HID 0.95
                              driver.version.internal: 0.38
                              input.sensitivity: medium
                              input.transfer.high: 139
                              input.transfer.low: 92
                              input.voltage: 126.0
                              input.voltage.nominal: 120
                              ups.beeper.status: enabled
                              ups.delay.shutdown: 20
                              ups.firmware: 904.W1 .D
                              ups.firmware.aux: W1
                              ups.load: 13
                              ups.mfr: APC
                              ups.mfr.date: 2014/06/22
                              ups.model: Back-UPS ES 550G
                              ups.productid: 0002
                              ups.serial: 4B1425P54201
                              ups.status: OL
                              ups.timer.reboot: 0
                              ups.timer.shutdown: -1
                              ups.vendorid: 051d
                              

                              Since reboot, the monitor has been running all the time. So it may have been simply that.

                              As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                              Take the output of upsc and throw it up on a web page. Unless you want a local display, in which case it's actually more difficult.

                              1 Reply Last reply Reply Quote 0
                              • thwrT
                                thwr @gjacobse
                                last edited by

                                @gjacobse said in Pi as a UPS monitor:

                                checking on my UPS this morning

                                 ~ $ uptime
                                 09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                                
                                 ~ $ sudo upsc pandora
                                Init SSL without certificate database
                                battery.charge: 100
                                battery.charge.low: 10
                                battery.charge.warning: 50
                                battery.date: not set
                                battery.mfr.date: 2014/06/22
                                battery.runtime: 3172
                                battery.runtime.low: 120
                                battery.type: PbAc
                                battery.voltage: 13.6
                                battery.voltage.nominal: 12.0
                                device.mfr: APC
                                device.model: Back-UPS ES 550G
                                device.serial: 4B1425P54201
                                device.type: ups
                                driver.name: usbhid-ups
                                driver.parameter.pollfreq: 30
                                driver.parameter.pollinterval: 2
                                driver.parameter.port: auto
                                driver.version: 2.7.1
                                driver.version.data: APC HID 0.95
                                driver.version.internal: 0.38
                                input.sensitivity: medium
                                input.transfer.high: 139
                                input.transfer.low: 92
                                input.voltage: 126.0
                                input.voltage.nominal: 120
                                ups.beeper.status: enabled
                                ups.delay.shutdown: 20
                                ups.firmware: 904.W1 .D
                                ups.firmware.aux: W1
                                ups.load: 13
                                ups.mfr: APC
                                ups.mfr.date: 2014/06/22
                                ups.model: Back-UPS ES 550G
                                ups.productid: 0002
                                ups.serial: 4B1425P54201
                                ups.status: OL
                                ups.timer.reboot: 0
                                ups.timer.shutdown: -1
                                ups.vendorid: 051d
                                

                                Since reboot, the monitor has been running all the time. So it may have been simply that.

                                As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                AMQP / MQTT may be awesome for this at the transport layer. MQTT is an interesting protocol that let you define a "last will and testament" action in case something goes south.

                                Ansible/Puppet etc. can handle the central configuration.

                                1 Reply Last reply Reply Quote 1
                                • JaredBuschJ
                                  JaredBusch
                                  last edited by

                                  Hey 3 months later.....

                                  1 Reply Last reply Reply Quote 1
                                  • JaredBuschJ
                                    JaredBusch
                                    last edited by

                                    Alright, I plugged the thing back in and got to testing.

                                    Yeah! It still communicates.

                                    pi@raspberrypi:~ $ sudo upsc jaredoffice
                                    Init SSL without certificate database
                                    battery.charge: 84
                                    battery.charge.low: 10
                                    battery.charge.warning: 50
                                    battery.date: 2001/09/25
                                    battery.mfr.date: 2010/12/15
                                    battery.runtime: 1236
                                    battery.runtime.low: 120
                                    battery.type: PbAc
                                    battery.voltage: 27.0
                                    battery.voltage.nominal: 24.0
                                    device.mfr: American Power Conversion
                                    device.model: Back-UPS BR1000G
                                    device.serial: 3B1051X20329
                                    device.type: ups
                                    driver.name: usbhid-ups
                                    driver.parameter.pollfreq: 30
                                    driver.parameter.pollinterval: 2
                                    driver.parameter.port: auto
                                    driver.version: 2.7.2
                                    driver.version.data: APC HID 0.95
                                    driver.version.internal: 0.38
                                    input.sensitivity: medium
                                    input.transfer.high: 147
                                    input.transfer.low: 88
                                    input.transfer.reason: input voltage out of range
                                    input.voltage: 124.0
                                    input.voltage.nominal: 120
                                    ups.beeper.status: enabled
                                    ups.delay.shutdown: 20
                                    ups.firmware: 868.L1 .D
                                    ups.firmware.aux: L1
                                    ups.load: 20
                                    ups.mfr: American Power Conversion
                                    ups.mfr.date: 2010/12/15
                                    ups.model: Back-UPS BR1000G
                                    ups.productid: 0002
                                    ups.realpower.nominal: 600
                                    ups.serial: 3B1051X20329
                                    ups.status: OL CHRG
                                    ups.test.result: No test initiated
                                    ups.timer.reboot: 0
                                    ups.timer.shutdown: -1
                                    ups.vendorid: 051d
                                    
                                    1 Reply Last reply Reply Quote 3
                                    • JaredBuschJ
                                      JaredBusch
                                      last edited by JaredBusch

                                      Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                                      Ok back to the manual and checking the conf files.

                                      Well it would probably help if I told the thing what to monitor..
                                      /etc/nut/upsmon.conf

                                      MONITOR jaredoffice@localhost 1 upsmon demo master
                                      

                                      Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                                      pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                                      # put at end of file
                                      [upsmon]
                                      password = demo
                                      upsmon master
                                      

                                      Now reload the monitor

                                      pi@raspberrypi:~ $ sudo upsmon -c reload
                                      Network UPS Tools upsmon 2.7.2
                                      pi@raspberrypi:~ $
                                      

                                      Then unplug the UPS. and get nothing.

                                      look in the logs..
                                      tail/var/log/syslog

                                      Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                                      Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                                      Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                                      Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                                      Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                                      

                                      Say to yourself, WTF did I do 3 months ago....

                                      Time to reload and start over.

                                      gjacobseG 1 Reply Last reply Reply Quote 0
                                      • gjacobseG
                                        gjacobse @JaredBusch
                                        last edited by

                                        @JaredBusch said in Pi as a UPS monitor:

                                        Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                                        Ok back to the manual and checking the conf files.

                                        Well it would probably help if I told the thing what to monitor..
                                        /etc/nut/upsmon.conf

                                        MONITOR jaredoffice@localhost 1 upsmon demo master
                                        

                                        Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                                        pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                                        # put at end of file
                                        [upsmon]
                                        password = demo
                                        upsmon master
                                        

                                        Now reload the monitor

                                        pi@raspberrypi:~ $ sudo upsmon -c reload
                                        Network UPS Tools upsmon 2.7.2
                                        pi@raspberrypi:~ $
                                        

                                        Then unplug the UPS. and get nothing.

                                        look in the logs..
                                        tail/var/log/syslog

                                        Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                                        Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                                        Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                                        Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                                        Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                                        

                                        Say to yourself, WTF did I do 3 months ago....

                                        Time to reload and start over.

                                        think i got the same thing, and decide the same course of action, to which I have not moved forward with. Albeit, it's not on a rPi but a desktop - premise is the same.

                                        Think we may have to create a user for the NUT system.... but again,.. can't work with it right now.

                                        1 Reply Last reply Reply Quote 0
                                        • JaredBuschJ
                                          JaredBusch
                                          last edited by JaredBusch

                                          Quick check of upsmon.conf found this, uncommented it.

                                          # RUN_AS_USER nut
                                          

                                          Rebooted Pi, unplugged UPS.

                                          Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:04 2017):
                                          
                                          UPS jaredoffice@localhost on battery
                                          
                                          
                                          Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:24 2017):
                                          
                                          UPS jaredoffice@localhost on line power
                                          
                                          1 Reply Last reply Reply Quote 0
                                          • JaredBuschJ
                                            JaredBusch
                                            last edited by

                                            Syslog had this though.

                                            Feb  1 17:19:04 raspberrypi upsmon[734]: UPS jaredoffice@localhost on battery
                                            Feb  1 17:19:11 raspberrypi upssched[792]: Failed to connect to parent and failed to create parent: No such file or directory
                                            Feb  1 17:19:24 raspberrypi upsmon[734]: UPS jaredoffice@localhost on line power
                                            

                                            Back to the config files we go!
                                            /etc/nut/upssched.conf

                                            # PIPEFN <filename>
                                            # This is commented out by default to make you visit this file and think
                                            # about how your system works before potentially opening a hole.
                                            

                                            FFS, but it gets better! Right below that, also commented out.

                                            # LOCKFN <filename>
                                            #
                                            # REQUIRED.  This was added after version 1.2.1.
                                            #
                                            # upssched needs to be able to create this filename in order to avoid
                                            # a race condition when two events are dispatched from upsmon at nearly
                                            # the same time.  This file will only exist briefly.  It must not be
                                            # created by any other process.
                                            #
                                            # You should put this in the same directory as PIPEFN.
                                            #
                                            

                                            So I update the config and make a directory forgetting to chown it from root /sigh...

                                            PIPEFN /etc/nut/upssched/upssched.pipe
                                            LOCKFN /etc/nut/upssched/upssched.lock
                                            1 Reply Last reply Reply Quote 0