    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • gjacobseG
      gjacobse @JaredBusch
      last edited by

      @JaredBusch said in Pi as a UPS monitor:

      Now to see if I can get time to work on this before next week.

      https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

      We are waiting with baited breath....

      travisdh1T 1 Reply Last reply Reply Quote 0
      • travisdh1T
        travisdh1 @gjacobse
        last edited by

        @gjacobse said in Pi as a UPS monitor:

        @JaredBusch said in Pi as a UPS monitor:

        Now to see if I can get time to work on this before next week.

        https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

        We are waiting with baited breath....

        I sense doubt, doubt leads to the dark side. Do or do not, @JaredBusch does not try.

        1 Reply Last reply Reply Quote 1
        • JaredBuschJ
          JaredBusch
          last edited by

          pi@raspberrypi:~ $ sudo upsc jaredoffice@localhost
          Init SSL without certificate database
          battery.charge: 100
          battery.charge.low: 10
          battery.charge.warning: 50
          battery.date: 2001/09/25
          battery.mfr.date: 2010/12/15
          battery.runtime: 1580
          battery.runtime.low: 120
          battery.type: PbAc
          battery.voltage: 27.2
          battery.voltage.nominal: 24.0
          device.mfr: American Power Conversion
          device.model: Back-UPS BR1000G
          device.serial: 3B1051X20329
          device.type: ups
          driver.name: usbhid-ups
          driver.parameter.pollfreq: 30
          driver.parameter.pollinterval: 2
          driver.parameter.port: auto
          driver.version: 2.7.2
          driver.version.data: APC HID 0.95
          driver.version.internal: 0.38
          input.sensitivity: medium
          input.transfer.high: 147
          input.transfer.low: 88
          input.voltage: 126.0
          input.voltage.nominal: 120
          ups.beeper.status: enabled
          ups.delay.shutdown: 20
          ups.firmware: 868.L1 .D
          ups.firmware.aux: L1
          ups.load: 18
          ups.mfr: American Power Conversion
          ups.mfr.date: 2010/12/15
          ups.model: Back-UPS BR1000G
          ups.productid: 0002
          ups.realpower.nominal: 600
          ups.serial: 3B1051X20329
          ups.status: OL
          ups.test.result: No test initiated
          ups.timer.reboot: 0
          ups.timer.shutdown: -1
          ups.vendorid: 051d
          pi@raspberrypi:~ $
          
          1 Reply Last reply Reply Quote 2
          • JaredBuschJ
            JaredBusch
            last edited by

            Hopefully I can get it to do something tomorrow. no more time tonight.

            1 Reply Last reply Reply Quote 0
            • JaredBuschJ
              JaredBusch
              last edited by JaredBusch

              Instructions assuming a Pi3

              1. Install NOOBS to the SD Card.
              2. Boot the Pi to NOOBS
              3. Connect to wifi
              4. Once it sees internet you can choose to install a minimal version of raspbian with no GUI
              5. wait
              6. login with default creds pi/raspberry
              7. run sudo raspi-config to enable SSH and optionally set other options you want.
              8. edit the wifi config file sudo nano /etc/wpa_supplicant/wpa_supplicant.conf
                network={
                ssid="yourssid"
                psk="ssidpassword"
                }
              9. reboot the Pi3
              10. update raspian
                1. sudo apt-get update
                2. sudo apt-get upgrade
              11. Install nut
                1. sudo apt-get install nut
              12. Edit sudo nano /etc/nut/nut.conf
                1. change MODE=standalone
              13. Edit sudo nano /etc/nut/ups.conf
              14. add a block at the end of the file.
                1. a default example
                  [somenameforups]
                  driver = usbhid-ups
                  port = auto
                  desc = "Some descriptive name for UPS"
                2. what mine is
                  [jaredoffice]
                  driver = usbhid-ups
                  port = auto
                  desc = "Jared's Desk"
              15. Test the conf file is right sudo upsdrvctl start
              16. Launch the UPS daemon sudo upsd
              17. see if it is talking sudo upsc somenameforups@localhost
                1. or my real one sudo upsc jaredoffice@localhost
              1 Reply Last reply Reply Quote 3
              • gjacobseG
                gjacobse
                last edited by

                Interesting that the last two of the last three messages seem out of order. But - great information.

                1 Reply Last reply Reply Quote 0
                • gjacobseG
                  gjacobse
                  last edited by gjacobse

                  Well - while I don't have a Pi yet, I do happen to have a LM 17.x system running as my Pandora Music box (Pithos). It's within reach of one of the several UPS units I have (I have like nine) so I used your process and got one set up:

                  sudo upsc pandora
                  :
                  Init SSL without certificate database
                  battery.charge: 100
                  battery.charge.low: 10
                  battery.charge.warning: 50
                  battery.date: not set
                  battery.mfr.date: 2014/06/22
                  battery.runtime: 3336
                  battery.runtime.low: 120
                  battery.type: PbAc
                  battery.voltage: 13.5
                  battery.voltage.nominal: 12.0
                  device.mfr: APC
                  device.model: Back-UPS ES 550G
                  device.serial: 4B1425P54201
                  device.type: ups
                  driver.name: usbhid-ups
                  driver.parameter.pollfreq: 30
                  driver.parameter.pollinterval: 2
                  driver.parameter.port: auto
                  driver.version: 2.7.1
                  driver.version.data: APC HID 0.95
                  driver.version.internal: 0.38
                  input.sensitivity: medium
                  input.transfer.high: 139
                  input.transfer.low: 92
                  input.voltage: 125.0
                  input.voltage.nominal: 120
                  ups.beeper.status: enabled
                  ups.delay.shutdown: 20
                  ups.firmware: 904.W1 .D
                  ups.firmware.aux: W1
                  ups.load: 12
                  ups.mfr: APC
                  ups.mfr.date: 2014/06/22
                  ups.model: Back-UPS ES 550G
                  ups.productid: 0002
                  ups.serial: 4B1425P54201
                  ups.status: OL
                  ups.timer.reboot: 0
                  ups.timer.shutdown: -1
                  ups.vendorid: 051d
                  
                  1 Reply Last reply Reply Quote 1
                  • JaredBuschJ
                    JaredBusch
                    last edited by

                    Today will be tinkering with notification options.

                    1 Reply Last reply Reply Quote 2
                    • gjacobseG
                      gjacobse
                      last edited by

                      Just got this:

                      Init SSL without certificate database
                      Error: Data stale
                      
                      1 Reply Last reply Reply Quote 0
                      • gjacobseG
                        gjacobse
                        last edited by

                        Went back through the commands above to validation / confirmation:

                        $ sudo nano /etc/nut/nut.conf
                        

                        no changes - the same.

                        $ sudo nano /etc/nut/ups.conf
                        

                        no changes - the same

                         $ sudo upsdrvctl start
                        Network UPS Tools - UPS driver controller 2.7.1
                        Network UPS Tools - Generic HID driver 0.38 (2.7.1)
                        USB communication driver 0.32
                        Duplicate driver instance detected! Terminating other driver!
                        Using subdriver: APC HID 0.95
                        

                        Okay - seems 'ok'

                        $ sudo upsd
                        Network UPS Tools upsd 2.7.1
                        fopen /var/run/nut/upsd.pid: No such file or directory
                        not listening on 127.0.0.1 port 3493
                        not listening on ::1 port 3493
                        no listening interface available
                        
                        $ sudo upsc pandora
                        Init SSL without certificate database
                        Error: Data stale
                        

                        curious.

                        JaredBuschJ 1 Reply Last reply Reply Quote 0
                        • JaredBuschJ
                          JaredBusch @gjacobse
                          last edited by

                          @gjacobse I do not get that. Mine has been untouched since last night.

                          pi@raspberrypi:~ $ sudo upsc jaredoffice
                          Init SSL without certificate database
                          battery.charge: 100
                          battery.charge.low: 10
                          battery.charge.warning: 50
                          battery.date: 2001/09/25
                          battery.mfr.date: 2010/12/15
                          battery.runtime: 1472
                          battery.runtime.low: 120
                          battery.type: PbAc
                          battery.voltage: 27.2
                          battery.voltage.nominal: 24.0
                          device.mfr: American Power Conversion
                          device.model: Back-UPS BR1000G
                          device.serial: 3B1051X20329
                          device.type: ups
                          driver.name: usbhid-ups
                          driver.parameter.pollfreq: 30
                          driver.parameter.pollinterval: 2
                          driver.parameter.port: auto
                          driver.version: 2.7.2
                          driver.version.data: APC HID 0.95
                          driver.version.internal: 0.38
                          input.sensitivity: medium
                          input.transfer.high: 147
                          input.transfer.low: 88
                          input.voltage: 124.0
                          input.voltage.nominal: 120
                          ups.beeper.status: enabled
                          ups.delay.shutdown: 20
                          ups.firmware: 868.L1 .D
                          ups.firmware.aux: L1
                          ups.load: 20
                          ups.mfr: American Power Conversion
                          ups.mfr.date: 2010/12/15
                          ups.model: Back-UPS BR1000G
                          ups.productid: 0002
                          ups.realpower.nominal: 600
                          ups.serial: 3B1051X20329
                          ups.status: OL
                          ups.test.result: No test initiated
                          ups.timer.reboot: 0
                          ups.timer.shutdown: -1
                          ups.vendorid: 051d
                          pi@raspberrypi:~ $
                          
                          1 Reply Last reply Reply Quote 0
                          • JaredBuschJ
                            JaredBusch
                            last edited by

                            This is what I will be following to configure reporting/alerting.
                            http://www.techrepublic.com/article/customize-ups-related-alerts-in-nut/

                            gjacobseG 1 Reply Last reply Reply Quote 1
                            • gjacobseG
                              gjacobse @JaredBusch
                              last edited by

                              @JaredBusch
                              Well push comes to Meh -okay. I restarted the box and it's polls now.

                              Won't do anything else with it for a spell to see if it retains it. It's been four days since I restarted it. Now - to reconnect to it as I had to pull the monitor off. X2Go works great,.. but only once I've signed in at the local. sure that is omething that can be changed.

                              1 Reply Last reply Reply Quote 0
                              • gjacobseG
                                gjacobse
                                last edited by

                                checking on my UPS this morning

                                 ~ $ uptime
                                 09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                                
                                 ~ $ sudo upsc pandora
                                Init SSL without certificate database
                                battery.charge: 100
                                battery.charge.low: 10
                                battery.charge.warning: 50
                                battery.date: not set
                                battery.mfr.date: 2014/06/22
                                battery.runtime: 3172
                                battery.runtime.low: 120
                                battery.type: PbAc
                                battery.voltage: 13.6
                                battery.voltage.nominal: 12.0
                                device.mfr: APC
                                device.model: Back-UPS ES 550G
                                device.serial: 4B1425P54201
                                device.type: ups
                                driver.name: usbhid-ups
                                driver.parameter.pollfreq: 30
                                driver.parameter.pollinterval: 2
                                driver.parameter.port: auto
                                driver.version: 2.7.1
                                driver.version.data: APC HID 0.95
                                driver.version.internal: 0.38
                                input.sensitivity: medium
                                input.transfer.high: 139
                                input.transfer.low: 92
                                input.voltage: 126.0
                                input.voltage.nominal: 120
                                ups.beeper.status: enabled
                                ups.delay.shutdown: 20
                                ups.firmware: 904.W1 .D
                                ups.firmware.aux: W1
                                ups.load: 13
                                ups.mfr: APC
                                ups.mfr.date: 2014/06/22
                                ups.model: Back-UPS ES 550G
                                ups.productid: 0002
                                ups.serial: 4B1425P54201
                                ups.status: OL
                                ups.timer.reboot: 0
                                ups.timer.shutdown: -1
                                ups.vendorid: 051d
                                

                                Since reboot, the monitor has been running all the time. So it may have been simply that.

                                As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                gjacobseG travisdh1T thwrT 3 Replies Last reply Reply Quote 1
                                • gjacobseG
                                  gjacobse @gjacobse
                                  last edited by

                                  @gjacobse said in Pi as a UPS monitor:

                                  checking on my UPS this morning

                                  Since reboot, the monitor has been running all the time. So it may have been simply that.

                                  As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                  Maybe something similar to the UBNT controller software - central configuration ability.....

                                  1 Reply Last reply Reply Quote 0
                                  • travisdh1T
                                    travisdh1 @gjacobse
                                    last edited by

                                    @gjacobse said in Pi as a UPS monitor:

                                    checking on my UPS this morning

                                     ~ $ uptime
                                     09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                                    
                                     ~ $ sudo upsc pandora
                                    Init SSL without certificate database
                                    battery.charge: 100
                                    battery.charge.low: 10
                                    battery.charge.warning: 50
                                    battery.date: not set
                                    battery.mfr.date: 2014/06/22
                                    battery.runtime: 3172
                                    battery.runtime.low: 120
                                    battery.type: PbAc
                                    battery.voltage: 13.6
                                    battery.voltage.nominal: 12.0
                                    device.mfr: APC
                                    device.model: Back-UPS ES 550G
                                    device.serial: 4B1425P54201
                                    device.type: ups
                                    driver.name: usbhid-ups
                                    driver.parameter.pollfreq: 30
                                    driver.parameter.pollinterval: 2
                                    driver.parameter.port: auto
                                    driver.version: 2.7.1
                                    driver.version.data: APC HID 0.95
                                    driver.version.internal: 0.38
                                    input.sensitivity: medium
                                    input.transfer.high: 139
                                    input.transfer.low: 92
                                    input.voltage: 126.0
                                    input.voltage.nominal: 120
                                    ups.beeper.status: enabled
                                    ups.delay.shutdown: 20
                                    ups.firmware: 904.W1 .D
                                    ups.firmware.aux: W1
                                    ups.load: 13
                                    ups.mfr: APC
                                    ups.mfr.date: 2014/06/22
                                    ups.model: Back-UPS ES 550G
                                    ups.productid: 0002
                                    ups.serial: 4B1425P54201
                                    ups.status: OL
                                    ups.timer.reboot: 0
                                    ups.timer.shutdown: -1
                                    ups.vendorid: 051d
                                    

                                    Since reboot, the monitor has been running all the time. So it may have been simply that.

                                    As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                    Take the output of upsc and throw it up on a web page. Unless you want a local display, in which case it's actually more difficult.

                                    1 Reply Last reply Reply Quote 0
                                    • thwrT
                                      thwr @gjacobse
                                      last edited by

                                      @gjacobse said in Pi as a UPS monitor:

                                      checking on my UPS this morning

                                       ~ $ uptime
                                       09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                                      
                                       ~ $ sudo upsc pandora
                                      Init SSL without certificate database
                                      battery.charge: 100
                                      battery.charge.low: 10
                                      battery.charge.warning: 50
                                      battery.date: not set
                                      battery.mfr.date: 2014/06/22
                                      battery.runtime: 3172
                                      battery.runtime.low: 120
                                      battery.type: PbAc
                                      battery.voltage: 13.6
                                      battery.voltage.nominal: 12.0
                                      device.mfr: APC
                                      device.model: Back-UPS ES 550G
                                      device.serial: 4B1425P54201
                                      device.type: ups
                                      driver.name: usbhid-ups
                                      driver.parameter.pollfreq: 30
                                      driver.parameter.pollinterval: 2
                                      driver.parameter.port: auto
                                      driver.version: 2.7.1
                                      driver.version.data: APC HID 0.95
                                      driver.version.internal: 0.38
                                      input.sensitivity: medium
                                      input.transfer.high: 139
                                      input.transfer.low: 92
                                      input.voltage: 126.0
                                      input.voltage.nominal: 120
                                      ups.beeper.status: enabled
                                      ups.delay.shutdown: 20
                                      ups.firmware: 904.W1 .D
                                      ups.firmware.aux: W1
                                      ups.load: 13
                                      ups.mfr: APC
                                      ups.mfr.date: 2014/06/22
                                      ups.model: Back-UPS ES 550G
                                      ups.productid: 0002
                                      ups.serial: 4B1425P54201
                                      ups.status: OL
                                      ups.timer.reboot: 0
                                      ups.timer.shutdown: -1
                                      ups.vendorid: 051d
                                      

                                      Since reboot, the monitor has been running all the time. So it may have been simply that.

                                      As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                      AMQP / MQTT may be awesome for this at the transport layer. MQTT is an interesting protocol that let you define a "last will and testament" action in case something goes south.

                                      Ansible/Puppet etc. can handle the central configuration.

                                      1 Reply Last reply Reply Quote 1
                                      • JaredBuschJ
                                        JaredBusch
                                        last edited by

                                        Hey 3 months later.....

                                        1 Reply Last reply Reply Quote 1
                                        • JaredBuschJ
                                          JaredBusch
                                          last edited by

                                          Alright, I plugged the thing back in and got to testing.

                                          Yeah! It still communicates.

                                          pi@raspberrypi:~ $ sudo upsc jaredoffice
                                          Init SSL without certificate database
                                          battery.charge: 84
                                          battery.charge.low: 10
                                          battery.charge.warning: 50
                                          battery.date: 2001/09/25
                                          battery.mfr.date: 2010/12/15
                                          battery.runtime: 1236
                                          battery.runtime.low: 120
                                          battery.type: PbAc
                                          battery.voltage: 27.0
                                          battery.voltage.nominal: 24.0
                                          device.mfr: American Power Conversion
                                          device.model: Back-UPS BR1000G
                                          device.serial: 3B1051X20329
                                          device.type: ups
                                          driver.name: usbhid-ups
                                          driver.parameter.pollfreq: 30
                                          driver.parameter.pollinterval: 2
                                          driver.parameter.port: auto
                                          driver.version: 2.7.2
                                          driver.version.data: APC HID 0.95
                                          driver.version.internal: 0.38
                                          input.sensitivity: medium
                                          input.transfer.high: 147
                                          input.transfer.low: 88
                                          input.transfer.reason: input voltage out of range
                                          input.voltage: 124.0
                                          input.voltage.nominal: 120
                                          ups.beeper.status: enabled
                                          ups.delay.shutdown: 20
                                          ups.firmware: 868.L1 .D
                                          ups.firmware.aux: L1
                                          ups.load: 20
                                          ups.mfr: American Power Conversion
                                          ups.mfr.date: 2010/12/15
                                          ups.model: Back-UPS BR1000G
                                          ups.productid: 0002
                                          ups.realpower.nominal: 600
                                          ups.serial: 3B1051X20329
                                          ups.status: OL CHRG
                                          ups.test.result: No test initiated
                                          ups.timer.reboot: 0
                                          ups.timer.shutdown: -1
                                          ups.vendorid: 051d
                                          
                                          1 Reply Last reply Reply Quote 3
                                          • JaredBuschJ
                                            JaredBusch
                                            last edited by JaredBusch

                                            Pulled the power cord from the wall. UPS beeps, but nothing from nut.

                                            Ok back to the manual and checking the conf files.

                                            Well it would probably help if I told the thing what to monitor..
                                            /etc/nut/upsmon.conf

                                            MONITOR jaredoffice@localhost 1 upsmon demo master
                                            

                                            Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

                                            pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
                                            # put at end of file
                                            [upsmon]
                                            password = demo
                                            upsmon master
                                            

                                            Now reload the monitor

                                            pi@raspberrypi:~ $ sudo upsmon -c reload
                                            Network UPS Tools upsmon 2.7.2
                                            pi@raspberrypi:~ $
                                            

                                            Then unplug the UPS. and get nothing.

                                            look in the logs..
                                            tail/var/log/syslog

                                            Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
                                            Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
                                            Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
                                            Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
                                            Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
                                            

                                            Say to yourself, WTF did I do 3 months ago....

                                            Time to reload and start over.

                                            gjacobseG 1 Reply Last reply Reply Quote 0