    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • gjacobseG
      gjacobse @JaredBusch
      last edited by

      @JaredBusch said in Pi as a UPS monitor:

      So ordering this one today.
      0_1475504077029_upload-aa8ddcff-9cac-498e-b4cb-3ea84837d1d0

      Why a 32GB card? Just because the cost is like - nothing?

      JaredBuschJ 1 Reply Last reply Reply Quote 0
      • JaredBuschJ
        JaredBusch @gjacobse
        last edited by

        @gjacobse said in Pi as a UPS monitor:

        @JaredBusch said in Pi as a UPS monitor:

        So ordering this one today.
        0_1475504077029_upload-aa8ddcff-9cac-498e-b4cb-3ea84837d1d0

        Why a 32GB card? Just because the cost is like - nothing?

        Because Amazon recommended it and I did not want to spend even 5 seconds finding my own card.

        Also This one will be used for a few more things than just the UPS monitor after I work out that process and figure our what device to buy multiples of.

        gjacobseG 1 Reply Last reply Reply Quote 2
        • gjacobseG
          gjacobse @JaredBusch
          last edited by

          @JaredBusch said in Pi as a UPS monitor:

          Why a 32GB card? Just because the cost is like - nothing?

          Because Amazon recommended it and I did not want to spend even 5 seconds finding my own card.

          Also This one will be used for a few more things than just the UPS monitor after I work out that process and figure our what device to buy multiples of.

          understandable.

          1 Reply Last reply Reply Quote 0
          • JaredBuschJ
            JaredBusch
            last edited by

            Now to see if I can get time to work on this before next week.

            https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

            gjacobseG 1 Reply Last reply Reply Quote 2
            • gjacobseG
              gjacobse @JaredBusch
              last edited by

              @JaredBusch said in Pi as a UPS monitor:

              Now to see if I can get time to work on this before next week.

              https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

              We are waiting with baited breath....

              travisdh1T 1 Reply Last reply Reply Quote 0
              • travisdh1T
                travisdh1 @gjacobse
                last edited by

                @gjacobse said in Pi as a UPS monitor:

                @JaredBusch said in Pi as a UPS monitor:

                Now to see if I can get time to work on this before next week.

                https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

                We are waiting with baited breath....

                I sense doubt, doubt leads to the dark side. Do or do not, @JaredBusch does not try.

                1 Reply Last reply Reply Quote 1
                • JaredBuschJ
                  JaredBusch
                  last edited by

                  pi@raspberrypi:~ $ sudo upsc jaredoffice@localhost
                  Init SSL without certificate database
                  battery.charge: 100
                  battery.charge.low: 10
                  battery.charge.warning: 50
                  battery.date: 2001/09/25
                  battery.mfr.date: 2010/12/15
                  battery.runtime: 1580
                  battery.runtime.low: 120
                  battery.type: PbAc
                  battery.voltage: 27.2
                  battery.voltage.nominal: 24.0
                  device.mfr: American Power Conversion
                  device.model: Back-UPS BR1000G
                  device.serial: 3B1051X20329
                  device.type: ups
                  driver.name: usbhid-ups
                  driver.parameter.pollfreq: 30
                  driver.parameter.pollinterval: 2
                  driver.parameter.port: auto
                  driver.version: 2.7.2
                  driver.version.data: APC HID 0.95
                  driver.version.internal: 0.38
                  input.sensitivity: medium
                  input.transfer.high: 147
                  input.transfer.low: 88
                  input.voltage: 126.0
                  input.voltage.nominal: 120
                  ups.beeper.status: enabled
                  ups.delay.shutdown: 20
                  ups.firmware: 868.L1 .D
                  ups.firmware.aux: L1
                  ups.load: 18
                  ups.mfr: American Power Conversion
                  ups.mfr.date: 2010/12/15
                  ups.model: Back-UPS BR1000G
                  ups.productid: 0002
                  ups.realpower.nominal: 600
                  ups.serial: 3B1051X20329
                  ups.status: OL
                  ups.test.result: No test initiated
                  ups.timer.reboot: 0
                  ups.timer.shutdown: -1
                  ups.vendorid: 051d
                  pi@raspberrypi:~ $
                  
                  1 Reply Last reply Reply Quote 2
                  • JaredBuschJ
                    JaredBusch
                    last edited by

                    Hopefully I can get it to do something tomorrow. no more time tonight.

                    1 Reply Last reply Reply Quote 0
                    • JaredBuschJ
                      JaredBusch
                      last edited by JaredBusch

                      Instructions assuming a Pi3

                      1. Install NOOBS to the SD Card.
                      2. Boot the Pi to NOOBS
                      3. Connect to wifi
                      4. Once it sees internet you can choose to install a minimal version of raspbian with no GUI
                      5. wait
                      6. login with default creds pi/raspberry
                      7. run sudo raspi-config to enable SSH and optionally set other options you want.
                      8. edit the wifi config file sudo nano /etc/wpa_supplicant/wpa_supplicant.conf
                        network={
                        ssid="yourssid"
                        psk="ssidpassword"
                        }
                      9. reboot the Pi3
                      10. update raspian
                        1. sudo apt-get update
                        2. sudo apt-get upgrade
                      11. Install nut
                        1. sudo apt-get install nut
                      12. Edit sudo nano /etc/nut/nut.conf
                        1. change MODE=standalone
                      13. Edit sudo nano /etc/nut/ups.conf
                      14. add a block at the end of the file.
                        1. a default example
                          [somenameforups]
                          driver = usbhid-ups
                          port = auto
                          desc = "Some descriptive name for UPS"
                        2. what mine is
                          [jaredoffice]
                          driver = usbhid-ups
                          port = auto
                          desc = "Jared's Desk"
                      15. Test the conf file is right sudo upsdrvctl start
                      16. Launch the UPS daemon sudo upsd
                      17. see if it is talking sudo upsc somenameforups@localhost
                        1. or my real one sudo upsc jaredoffice@localhost
                      1 Reply Last reply Reply Quote 3
                      • gjacobseG
                        gjacobse
                        last edited by

                        Interesting that the last two of the last three messages seem out of order. But - great information.

                        1 Reply Last reply Reply Quote 0
                        • gjacobseG
                          gjacobse
                          last edited by gjacobse

                          Well - while I don't have a Pi yet, I do happen to have a LM 17.x system running as my Pandora Music box (Pithos). It's within reach of one of the several UPS units I have (I have like nine) so I used your process and got one set up:

                          sudo upsc pandora
                          :
                          Init SSL without certificate database
                          battery.charge: 100
                          battery.charge.low: 10
                          battery.charge.warning: 50
                          battery.date: not set
                          battery.mfr.date: 2014/06/22
                          battery.runtime: 3336
                          battery.runtime.low: 120
                          battery.type: PbAc
                          battery.voltage: 13.5
                          battery.voltage.nominal: 12.0
                          device.mfr: APC
                          device.model: Back-UPS ES 550G
                          device.serial: 4B1425P54201
                          device.type: ups
                          driver.name: usbhid-ups
                          driver.parameter.pollfreq: 30
                          driver.parameter.pollinterval: 2
                          driver.parameter.port: auto
                          driver.version: 2.7.1
                          driver.version.data: APC HID 0.95
                          driver.version.internal: 0.38
                          input.sensitivity: medium
                          input.transfer.high: 139
                          input.transfer.low: 92
                          input.voltage: 125.0
                          input.voltage.nominal: 120
                          ups.beeper.status: enabled
                          ups.delay.shutdown: 20
                          ups.firmware: 904.W1 .D
                          ups.firmware.aux: W1
                          ups.load: 12
                          ups.mfr: APC
                          ups.mfr.date: 2014/06/22
                          ups.model: Back-UPS ES 550G
                          ups.productid: 0002
                          ups.serial: 4B1425P54201
                          ups.status: OL
                          ups.timer.reboot: 0
                          ups.timer.shutdown: -1
                          ups.vendorid: 051d
                          
                          1 Reply Last reply Reply Quote 1
                          • JaredBuschJ
                            JaredBusch
                            last edited by

                            Today will be tinkering with notification options.

                            1 Reply Last reply Reply Quote 2
                            • gjacobseG
                              gjacobse
                              last edited by

                              Just got this:

                              Init SSL without certificate database
                              Error: Data stale
                              
                              1 Reply Last reply Reply Quote 0
                              • gjacobseG
                                gjacobse
                                last edited by

                                Went back through the commands above to validation / confirmation:

                                $ sudo nano /etc/nut/nut.conf
                                

                                no changes - the same.

                                $ sudo nano /etc/nut/ups.conf
                                

                                no changes - the same

                                 $ sudo upsdrvctl start
                                Network UPS Tools - UPS driver controller 2.7.1
                                Network UPS Tools - Generic HID driver 0.38 (2.7.1)
                                USB communication driver 0.32
                                Duplicate driver instance detected! Terminating other driver!
                                Using subdriver: APC HID 0.95
                                

                                Okay - seems 'ok'

                                $ sudo upsd
                                Network UPS Tools upsd 2.7.1
                                fopen /var/run/nut/upsd.pid: No such file or directory
                                not listening on 127.0.0.1 port 3493
                                not listening on ::1 port 3493
                                no listening interface available
                                
                                $ sudo upsc pandora
                                Init SSL without certificate database
                                Error: Data stale
                                

                                curious.

                                JaredBuschJ 1 Reply Last reply Reply Quote 0
                                • JaredBuschJ
                                  JaredBusch @gjacobse
                                  last edited by

                                  @gjacobse I do not get that. Mine has been untouched since last night.

                                  pi@raspberrypi:~ $ sudo upsc jaredoffice
                                  Init SSL without certificate database
                                  battery.charge: 100
                                  battery.charge.low: 10
                                  battery.charge.warning: 50
                                  battery.date: 2001/09/25
                                  battery.mfr.date: 2010/12/15
                                  battery.runtime: 1472
                                  battery.runtime.low: 120
                                  battery.type: PbAc
                                  battery.voltage: 27.2
                                  battery.voltage.nominal: 24.0
                                  device.mfr: American Power Conversion
                                  device.model: Back-UPS BR1000G
                                  device.serial: 3B1051X20329
                                  device.type: ups
                                  driver.name: usbhid-ups
                                  driver.parameter.pollfreq: 30
                                  driver.parameter.pollinterval: 2
                                  driver.parameter.port: auto
                                  driver.version: 2.7.2
                                  driver.version.data: APC HID 0.95
                                  driver.version.internal: 0.38
                                  input.sensitivity: medium
                                  input.transfer.high: 147
                                  input.transfer.low: 88
                                  input.voltage: 124.0
                                  input.voltage.nominal: 120
                                  ups.beeper.status: enabled
                                  ups.delay.shutdown: 20
                                  ups.firmware: 868.L1 .D
                                  ups.firmware.aux: L1
                                  ups.load: 20
                                  ups.mfr: American Power Conversion
                                  ups.mfr.date: 2010/12/15
                                  ups.model: Back-UPS BR1000G
                                  ups.productid: 0002
                                  ups.realpower.nominal: 600
                                  ups.serial: 3B1051X20329
                                  ups.status: OL
                                  ups.test.result: No test initiated
                                  ups.timer.reboot: 0
                                  ups.timer.shutdown: -1
                                  ups.vendorid: 051d
                                  pi@raspberrypi:~ $
                                  
                                  1 Reply Last reply Reply Quote 0
                                  • JaredBuschJ
                                    JaredBusch
                                    last edited by

                                    This is what I will be following to configure reporting/alerting.
                                    http://www.techrepublic.com/article/customize-ups-related-alerts-in-nut/

                                    gjacobseG 1 Reply Last reply Reply Quote 1
                                    • gjacobseG
                                      gjacobse @JaredBusch
                                      last edited by

                                      @JaredBusch
                                      Well push comes to Meh -okay. I restarted the box and it's polls now.

                                      Won't do anything else with it for a spell to see if it retains it. It's been four days since I restarted it. Now - to reconnect to it as I had to pull the monitor off. X2Go works great,.. but only once I've signed in at the local. sure that is omething that can be changed.

                                      1 Reply Last reply Reply Quote 0
                                      • gjacobseG
                                        gjacobse
                                        last edited by

                                        checking on my UPS this morning

                                         ~ $ uptime
                                         09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                                        
                                         ~ $ sudo upsc pandora
                                        Init SSL without certificate database
                                        battery.charge: 100
                                        battery.charge.low: 10
                                        battery.charge.warning: 50
                                        battery.date: not set
                                        battery.mfr.date: 2014/06/22
                                        battery.runtime: 3172
                                        battery.runtime.low: 120
                                        battery.type: PbAc
                                        battery.voltage: 13.6
                                        battery.voltage.nominal: 12.0
                                        device.mfr: APC
                                        device.model: Back-UPS ES 550G
                                        device.serial: 4B1425P54201
                                        device.type: ups
                                        driver.name: usbhid-ups
                                        driver.parameter.pollfreq: 30
                                        driver.parameter.pollinterval: 2
                                        driver.parameter.port: auto
                                        driver.version: 2.7.1
                                        driver.version.data: APC HID 0.95
                                        driver.version.internal: 0.38
                                        input.sensitivity: medium
                                        input.transfer.high: 139
                                        input.transfer.low: 92
                                        input.voltage: 126.0
                                        input.voltage.nominal: 120
                                        ups.beeper.status: enabled
                                        ups.delay.shutdown: 20
                                        ups.firmware: 904.W1 .D
                                        ups.firmware.aux: W1
                                        ups.load: 13
                                        ups.mfr: APC
                                        ups.mfr.date: 2014/06/22
                                        ups.model: Back-UPS ES 550G
                                        ups.productid: 0002
                                        ups.serial: 4B1425P54201
                                        ups.status: OL
                                        ups.timer.reboot: 0
                                        ups.timer.shutdown: -1
                                        ups.vendorid: 051d
                                        

                                        Since reboot, the monitor has been running all the time. So it may have been simply that.

                                        As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                        gjacobseG travisdh1T thwrT 3 Replies Last reply Reply Quote 1
                                        • gjacobseG
                                          gjacobse @gjacobse
                                          last edited by

                                          @gjacobse said in Pi as a UPS monitor:

                                          checking on my UPS this morning

                                          Since reboot, the monitor has been running all the time. So it may have been simply that.

                                          As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                          Maybe something similar to the UBNT controller software - central configuration ability.....

                                          1 Reply Last reply Reply Quote 0
                                          • travisdh1T
                                            travisdh1 @gjacobse
                                            last edited by

                                            @gjacobse said in Pi as a UPS monitor:

                                            checking on my UPS this morning

                                             ~ $ uptime
                                             09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                                            
                                             ~ $ sudo upsc pandora
                                            Init SSL without certificate database
                                            battery.charge: 100
                                            battery.charge.low: 10
                                            battery.charge.warning: 50
                                            battery.date: not set
                                            battery.mfr.date: 2014/06/22
                                            battery.runtime: 3172
                                            battery.runtime.low: 120
                                            battery.type: PbAc
                                            battery.voltage: 13.6
                                            battery.voltage.nominal: 12.0
                                            device.mfr: APC
                                            device.model: Back-UPS ES 550G
                                            device.serial: 4B1425P54201
                                            device.type: ups
                                            driver.name: usbhid-ups
                                            driver.parameter.pollfreq: 30
                                            driver.parameter.pollinterval: 2
                                            driver.parameter.port: auto
                                            driver.version: 2.7.1
                                            driver.version.data: APC HID 0.95
                                            driver.version.internal: 0.38
                                            input.sensitivity: medium
                                            input.transfer.high: 139
                                            input.transfer.low: 92
                                            input.voltage: 126.0
                                            input.voltage.nominal: 120
                                            ups.beeper.status: enabled
                                            ups.delay.shutdown: 20
                                            ups.firmware: 904.W1 .D
                                            ups.firmware.aux: W1
                                            ups.load: 13
                                            ups.mfr: APC
                                            ups.mfr.date: 2014/06/22
                                            ups.model: Back-UPS ES 550G
                                            ups.productid: 0002
                                            ups.serial: 4B1425P54201
                                            ups.status: OL
                                            ups.timer.reboot: 0
                                            ups.timer.shutdown: -1
                                            ups.vendorid: 051d
                                            

                                            Since reboot, the monitor has been running all the time. So it may have been simply that.

                                            As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                            Take the output of upsc and throw it up on a web page. Unless you want a local display, in which case it's actually more difficult.

                                            1 Reply Last reply Reply Quote 0