    stand by computers in server room

    IT Discussion
    12
    109
    39.3k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • thanksajdotcomT
      thanksajdotcom @IT-ADMIN
      last edited by

      @IT-ADMIN said:

      when i access server room, the metal looks wet, is this show that there is humidity right?

      Yup. And remember, even if it isn't full-on droplets of water, if you're getting enough moisture that it's starting to actually do to your motherboards what it's doing to the door, you have a SERIOUS problem. I'd start by at least putting some dehumidifiers in there until a more permanent solution can be arranged. Just bear in mind, those have to be emptied usually.

      1 Reply Last reply Reply Quote 0
      • scottalanmillerS
        scottalanmiller @IT-ADMIN
        last edited by

        @IT-ADMIN said:

        when i access server room, the metal looks wet, is this show that there is humidity right?

        Yeah. It should NEVER look wet. You need a hygrometer in there, always. You should not be guessing, you need to KNOW what the humidity is at all times, even more than the temperature (which you would feel if it got too hot.)

        1 Reply Last reply Reply Quote 0
        • scottalanmillerS
          scottalanmiller
          last edited by

          Why is your server room at 17 anyway? That is far, far below recommended temperatures.

          thanksajdotcomT 1 Reply Last reply Reply Quote 0
          • thanksajdotcomT
            thanksajdotcom @scottalanmiller
            last edited by

            @scottalanmiller said:

            Why is your server room at 17 anyway? That is far, far below recommended temperatures.

            And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

            scottalanmillerS 1 Reply Last reply Reply Quote 1
            • scottalanmillerS
              scottalanmiller @thanksajdotcom
              last edited by

              @thanksajdotcom said:

              @scottalanmiller said:

              Why is your server room at 17 anyway? That is far, far below recommended temperatures.

              And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

              Yup, I'd look at raising that at least to 25.

              IT-ADMINI 1 Reply Last reply Reply Quote 0
              • scottalanmillerS
                scottalanmiller
                last edited by

                Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                thanksajdotcomT 1 Reply Last reply Reply Quote 0
                • thanksajdotcomT
                  thanksajdotcom @scottalanmiller
                  last edited by

                  @scottalanmiller said:

                  Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                  Wow, that's 86-90F. That seems very warm!

                  coliverC scottalanmillerS 2 Replies Last reply Reply Quote 0
                  • IT-ADMINI
                    IT-ADMIN @scottalanmiller
                    last edited by

                    @scottalanmiller said:

                    @thanksajdotcom said:

                    @scottalanmiller said:

                    Why is your server room at 17 anyway? That is far, far below recommended temperatures.

                    And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

                    Yup, I'd look at raising that at least to 25.

                    the problem is the high temperature we have in qatar, usually 46 - 38 C, so if i raise the temperature, i risk to kill the servers

                    coliverC scottalanmillerS 2 Replies Last reply Reply Quote 0
                    • coliverC
                      coliver @thanksajdotcom
                      last edited by

                      @thanksajdotcom said:

                      @scottalanmiller said:

                      Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                      Wow, that's 86-90F. That seems very warm!

                      We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                      thanksajdotcomT scottalanmillerS 2 Replies Last reply Reply Quote 0
                      • coliverC
                        coliver @IT-ADMIN
                        last edited by

                        @IT-ADMIN said:

                        @scottalanmiller said:

                        @thanksajdotcom said:

                        @scottalanmiller said:

                        Why is your server room at 17 anyway? That is far, far below recommended temperatures.

                        And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

                        Yup, I'd look at raising that at least to 25.

                        the problem is the high temperature we have in qatar, usually 46 - 38 C, so if i raise the temperature, i risk to kill the servers

                        Your server room should have independent air conditioning. Keeping it around 20-25 C should be fine.

                        scottalanmillerS 1 Reply Last reply Reply Quote 1
                        • thanksajdotcomT
                          thanksajdotcom @coliver
                          last edited by

                          @coliver said:

                          @thanksajdotcom said:

                          @scottalanmiller said:

                          Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                          Wow, that's 86-90F. That seems very warm!

                          We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                          I guess that makes sense. I mean, as a mostly-human being, Syracuse during the summer is often infinitely harder to handle than Dallas ever was due to how humidity affects perception of temperature. I guess it wouldn't be THAT different to electronics.

                          scottalanmillerS 1 Reply Last reply Reply Quote 0
                          • scottalanmillerS
                            scottalanmiller @thanksajdotcom
                            last edited by

                            @thanksajdotcom said:

                            Wow, that's 86-90F. That seems very warm!

                            It sure does, because IT has this cultural obsession with thinking only in terms of the servers themselves and not holistically for the business. It's "IT at any cost" thinking. That and poor airflow forces datacenters to go with super cold air to make up for heated air pockets.

                            But servers do not need the cold air that IT generally assumes. That's a myth that just keeps getting repeated. Good airflow and holistic business thinking put the optimum temperatures much higher in cases where the cold air is not essentially free (like Scotland.)

                            1 Reply Last reply Reply Quote 0
                            • scottalanmillerS
                              scottalanmiller @coliver
                              last edited by

                              @coliver said:

                              @IT-ADMIN said:

                              @scottalanmiller said:

                              @thanksajdotcom said:

                              @scottalanmiller said:

                              Why is your server room at 17 anyway? That is far, far below recommended temperatures.

                              And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

                              Yup, I'd look at raising that at least to 25.

                              the problem is the high temperature we have in qatar, usually 46 - 38 C, so if i raise the temperature, i risk to kill the servers

                              Your server room should have independent air conditioning. Keeping it around 20-25 C should be fine.

                              What matters is keeping it consistent, not the temp itself.

                              1 Reply Last reply Reply Quote 2
                              • scottalanmillerS
                                scottalanmiller @IT-ADMIN
                                last edited by

                                @IT-ADMIN said:

                                @scottalanmiller said:

                                @thanksajdotcom said:

                                @scottalanmiller said:

                                Why is your server room at 17 anyway? That is far, far below recommended temperatures.

                                And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

                                Yup, I'd look at raising that at least to 25.

                                the problem is the high temperature we have in qatar, usually 46 - 38 C, so if i raise the temperature, i risk to kill the servers

                                That's NOT how air conditioning works. The temperature outside has nothing to do with the temperature inside. If you set it to 17, it is 17 no matter what the temp is outside. If you set it to 25, it is the same 25 as for any of us. Your 25 is not hotter than ours. What DOES matter is that the cost of cooling from 46 to 17 is much, much higher than cooling from 25 to 17. So the price for going unnecessarily low is more for you.

                                1 Reply Last reply Reply Quote 1
                                • scottalanmillerS
                                  scottalanmiller @coliver
                                  last edited by

                                  @coliver said:

                                  @thanksajdotcom said:

                                  @scottalanmiller said:

                                  Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                                  Wow, that's 86-90F. That seems very warm!

                                  We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                                  We've done these tests (nonvoluntarily) with HP servers and they ran happily towards 160F!! But I would not recommend it since humans can't go in the room to replace parts.

                                  1 Reply Last reply Reply Quote 0
                                  • scottalanmillerS
                                    scottalanmiller @thanksajdotcom
                                    last edited by

                                    @thanksajdotcom said:

                                    @coliver said:

                                    @thanksajdotcom said:

                                    @scottalanmiller said:

                                    Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                                    Wow, that's 86-90F. That seems very warm!

                                    We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                                    I guess that makes sense. I mean, as a mostly-human being, Syracuse during the summer is often infinitely harder to handle than Dallas ever was due to how humidity affects perception of temperature. I guess it wouldn't be THAT different to electronics.

                                    Although it is opposite, for electronics which are air cooled, high humidity increases cooling potential. For humans which are evaporation cooled, humidity decreases cooling potential.

                                    thanksajdotcomT 1 Reply Last reply Reply Quote 0
                                    • scottalanmillerS
                                      scottalanmiller
                                      last edited by

                                      IBM has shown that running at 37C consistently is far better for your gear than bouncing around between 15C and 20C.

                                      1 Reply Last reply Reply Quote 0
                                      • scottalanmillerS
                                        scottalanmiller
                                        last edited by

                                        Moving to SSDs actually makes it:

                                        • Easier to cool as there is less heat generated and less power drawn.
                                        • Temps can be higher than before.
                                        • Fluctuations are not as big of a risk.

                                        You can potentially save a lot of money with SSD for various reasons.

                                        1 Reply Last reply Reply Quote 1
                                        • thanksajdotcomT
                                          thanksajdotcom @scottalanmiller
                                          last edited by

                                          @scottalanmiller said:

                                          @thanksajdotcom said:

                                          @coliver said:

                                          @thanksajdotcom said:

                                          @scottalanmiller said:

                                          Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                                          Wow, that's 86-90F. That seems very warm!

                                          We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                                          I guess that makes sense. I mean, as a mostly-human being, Syracuse during the summer is often infinitely harder to handle than Dallas ever was due to how humidity affects perception of temperature. I guess it wouldn't be THAT different to electronics.

                                          Although it is opposite, for electronics which are air cooled, high humidity increases cooling potential. For humans which are evaporation cooled, humidity decreases cooling potential.

                                          Fair enough...still, water on a board due to condensation is a risk.

                                          scottalanmillerS 1 Reply Last reply Reply Quote 0
                                          • scottalanmillerS
                                            scottalanmiller @thanksajdotcom
                                            last edited by

                                            @thanksajdotcom said:

                                            @scottalanmiller said:

                                            @thanksajdotcom said:

                                            @coliver said:

                                            @thanksajdotcom said:

                                            @scottalanmiller said:

                                            Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                                            Wow, that's 86-90F. That seems very warm!

                                            We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                                            I guess that makes sense. I mean, as a mostly-human being, Syracuse during the summer is often infinitely harder to handle than Dallas ever was due to how humidity affects perception of temperature. I guess it wouldn't be THAT different to electronics.

                                            Although it is opposite, for electronics which are air cooled, high humidity increases cooling potential. For humans which are evaporation cooled, humidity decreases cooling potential.

                                            Fair enough...still, water on a board due to condensation is a risk.

                                            Oh yes, you can't let there be water, ever.

                                            1 Reply Last reply Reply Quote 0